trane xb80 not working at all
Hi
i have a trane xb80 furnace that was blowing cold air and as i read in this forum and according to the led code with flashing 4 times i found that i should change my swith limit , so i took out the switch it was l190f30 but the shop gave me l180f40 and told me it should work . I installed it on the furnace but it was blowing again colx air and whenever i was trying to put the temp above 23 it was stoping blowing air . And after a while it completely stop working . Now it's not working at alland it seams ghat there is no power in the furnace and the light is completely off . Please help we what to do ?
i have a trane xb80 furnace that was blowing cold air and as i read in this forum and according to the led code with flashing 4 times i found that i should change my swith limit , so i took out the switch it was l190f30 but the shop gave me l180f40 and told me it should work . I installed it on the furnace but it was blowing again colx air and whenever i was trying to put the temp above 23 it was stoping blowing air . And after a while it completely stop working . Now it's not working at alland it seams ghat there is no power in the furnace and the light is completely off . Please help we what to do ?
#17
There is nothing there , no fuse at that location as it shown in the photo
Can you provide the model number of the control board. It will be shown on the cover of the board as shown in post #5. The photo I attached in that post is the original part number for the XB80 furnace.
Last edited by firedawgsatx; 12-25-14 at 02:47 PM.
#21
If I'm not wrong D341828P01
No there is no sockets in that place.
Last edited by firedawgsatx; 12-25-14 at 04:53 PM.
#24
Ok, it appears to be one of the boards with just a wire instead of a fuse. You will need to test the voltage coming out of the transformer. Did you try to re-set the circuit breaker for the furnace to see if you can restore power?
#25
Member
Thread Starter
Join Date: Dec 2014
Posts: 27
Upvotes: 0
Received 0 Upvotes
on
0 Posts
How should i do that ? I dont know how to do that
if you mean reset it via electical panel , yes i did itthe number that i gave you before was the serial number
E
50A55-571
156-4341 rev.B
can it be the model number
if you mean reset it via electical panel , yes i did itthe number that i gave you before was the serial number
E
50A55-571
156-4341 rev.B
can it be the model number

Last edited by ebiabdi; 12-25-14 at 08:37 PM.
#26
Yes, the model number is 50A55-571. That is one of the boards that did not have a fuse installed on the board. When the board does not have a fuse a competent installer will wire in an in-line fuse to protect the transformer and low voltage wiring. If you follow the wires coming from the low voltage side of the transformer do you see what looks like a fuse holder? When I say you need to re-set the circuit breaker it will be inside the main electrical panel that provides power to the rest of your house. There should be a circuit breaker that is marked furnace. You will need to find that and turn it off and then back on to reset the furnace control board.
#30
If re-setting the breaker didn't reset the control board that's about all you can do until you can use a meter to test voltages. You will need to set the meter to volts AC and with the door switch pushed in test to see if you have 120V going in and 24V coming out of the transformer. If you have 120V going in but no voltage coming out your transformer is bad and will need to be replaced.
#32
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
I know it sounds really basic but sometimes we can't see the forrest for the trees:
Are you sure the emergency switch (usually ouside the furnace closet or at the top of the basement stairs) is on? How about another switch on or very near the furnace? Certainly can't hurt to double check.
Are you sure the emergency switch (usually ouside the furnace closet or at the top of the basement stairs) is on? How about another switch on or very near the furnace? Certainly can't hurt to double check.
#33
Member
Thread Starter
Join Date: Dec 2014
Posts: 27
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Hi , i Checked the transformer when the switch is on , the voltage coming in is 123 but there is no voltage coming out .
does it mean that the transformer should be changed ? Can it be fixed ?if not did the high limit switch cause the problem ? How can i test the transfomer seprately to besure that the transformer is completely down ?
Thanks again
does it mean that the transformer should be changed ? Can it be fixed ?if not did the high limit switch cause the problem ? How can i test the transfomer seprately to besure that the transformer is completely down ?
Thanks again
Last edited by ebiabdi; 12-26-14 at 11:16 AM.
#34
the voltage coming in is 123 but there is no voltage coming out. does it mean that the transformer should be changed?
did the high limit switch cause the problem ?
You stated you changed the limit switch. How did you determine it was the limit switch that caused the issue and threw a 4-flash code? Did you use a meter to verify if the switch was open or was it a guess. According to the wiring diagram you posted there are four thermal protection devices in your furnace: one limit, two non-reset (fusible link) rollout switches and a reverse flow switch. Now that you have a meter you can check for continuity to see if any of the switches is open.
The attached photos should be similar to the roll-out switches you have in your furnace. I also attached a wiring diagram that shows the thermal protection circuit with a yellow line designating the path.
Last edited by firedawgsatx; 12-26-14 at 01:45 PM. Reason: Added attachment
#35
Member
Thread Starter
Join Date: Dec 2014
Posts: 27
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks i checked ythem all and the switch limit was open , and for the fusible links and the other switch after about the test for the switches , it starts with 00.3 and after a few seconds it changed to 000 , is it OK
cheers
cheers
#36
the switch limit was open
and for the fusible links and the other switch after about the test for the switches , it starts with 00.3 and after a few seconds it changed to 000 , is it OK
#38
Both have this problem now they are not 0
#39
Member
Thread Starter
Join Date: Dec 2014
Posts: 27
Upvotes: 0
Received 0 Upvotes
on
0 Posts
i checked again the limit switches . The result was exactly when i touched the two leads 00.3 so does it mean that the all of the other switches . All of the switches are fine . So what ? Does the transformer was the only problem ? So how the furnace was just blowing cold air the error code was 4 ?
the reason of making the furnace to hot may be the filter as it had not been changed for a while and it was too dirty . But the problem of having cold air was for a while something around 2-3 weeks . Are you still saying that it was just for the filter and there were no more problem . What was the problem of stop to blow air after i had set the temp over 23 deg . And why after i had reset the furnace before and after changing the switch the switched hasn't been reset . I should add that after i changed the limit switch, the error code was call to heat and i didn't have flame .
the reason of making the furnace to hot may be the filter as it had not been changed for a while and it was too dirty . But the problem of having cold air was for a while something around 2-3 weeks . Are you still saying that it was just for the filter and there were no more problem . What was the problem of stop to blow air after i had set the temp over 23 deg . And why after i had reset the furnace before and after changing the switch the switched hasn't been reset . I should add that after i changed the limit switch, the error code was call to heat and i didn't have flame .
#40
If you have an a/c evaporator coil installed it could also be clogged because the air filter was dirty. If the limit switches test good then the furnace may operate properly after the transformer is replaced. Until that time you can only guess.