Natural gas furnace stuck on defrost, 2nd stage and won't heat.

Greetings,

I have a bi-energy heating system, Lincoln natural gaz furnace and a Kenmore (ICP, Model CHP224AKA1) heatpump controlled by a Sears thermostat.

During this time of the year, I set the thermostat on "emergency heat", which bypasses the heat pump and runs on furnace exclusively. My furnace started misbehaving a couple weeks ago, when I woke up to a cold house. It seems the furnace got stuck on 'defrost mode'. After turning the thermostat on/off a couple times, it started heating again like normal. It happened a couple other times and then it now it just won't start heating at all, on emergency heat or not. When on emergency heat, the 'aux' light comes on, and I hear a 'tick' sound, but the word 'heat' doesn't come up on the thermostat.

The furnace control panel shows no blinking light on start. The 'defrost', '2nd stage', and 'power' indicators are lit. I've tried bypassing the thermostat by wiring the R and W2 wires together, with same results. The furnace pilot glows a bright orange, but nothing happens. I'm pretty sure it shouldn't even try to defrost when on 'emergency mode'.

Any ideas of what I could look for?

Name:  20141227_155601.jpg
Views: 472
Size:  48.7 KBName:  20141226_113856.jpg
Views: 451
Size:  49.5 KBName:  20141226_113919.jpg
Views: 277
Size:  28.0 KBName:  20141226_114221.jpg
Views: 406
Size:  35.3 KBName:  20141227_170159.jpg
Views: 486
Size:  49.6 KB
 
Sponsored Links
  #2  
Old 12-27-14, 04:34 PM
Member
Join Date: Feb 2014
Location: USA
Posts: 2,104
Received 0 Votes on 0 Posts
You are right, when in emergency mode the heat pump won't run or defrost. Have you checked the power to the gas valve?
 
  #3  
Old 12-30-14, 11:06 AM
Member
Thread Starter
Join Date: Dec 2014
Location: Canada
Posts: 3
Received 0 Votes on 0 Posts
I tested power to the valve, it's around 26-28 VAC. The controls are also powered. There's a plastic cover that I removed to see if there was anything I could fix in the valve, but I'm not seeing anything abnormal there.

Faulty valve?

Name:  20141230_125501.jpg
Views: 320
Size:  43.9 KB
 
  #4  
Old 12-30-14, 03:38 PM
Member
Thread Starter
Join Date: Dec 2014
Location: Canada
Posts: 3
Received 0 Votes on 0 Posts
Problem was with the ignition. After changing it, I got a pilot flame, which I didn't have before, but the heat still wouldn't start, the flame was yellow and not stable. After cleaning, the tiny ignition hole, furnace finally started.
 
  #5  
Old 12-30-14, 06:06 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,943
Received 5 Votes on 5 Posts
Glad you got it up & running. As a side note, in your first picture of the thermostat, I don't like the looks of the wires as they come out of the wall. Maybe it's just dust or due to a lack of light but they look awfully dark as if they've been hot. Probably nothing but worth taking a look.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: