Help with Williams direct vent wall heater.

I'm having the same problem as the original poster. Williams direct-vent wall heater. The pilot light stays lit, but I can't get the heater to turn on.

Voltage is 260mV with the thermostat both on or off.

I removed the pilot tube and did my best to clean it, but no effect.

I think it was hooked up to a low voltage thermostat, but I just hooked it up to a millivolt thermostat.

Any ideas?


Separated from... http://www.doityourself.com/forum/ga...l-furnace.html
 

Last edited by PJmax; 01-03-15 at 04:19 PM. Reason: started new thread
  #2  
Old 01-03-15, 04:28 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,408
Received 1,405 Votes on 1,300 Posts
Welcome to the forums.

Hopefully you'll get my PM and follow us to your new thread.

Your voltage reading is very good. It tells us that your pilot generator is probably ok as well as your pilot flame.

When you activate your thermostat that 260mv should immediately drop to under 200mv or so. It sounds like your thermostat isn't making contact. You can take the two wires that go to the thermostat and short them together. That should bring the burner on.
 
  #3  
Old 01-03-15, 05:44 PM
O
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Thanks for your assistance. I just tried your test. Lit the pilot light and tested the voltage at 300mV. Shorted the TH/TP and TH terminals at the furnace, and the pilot light went out. What do you think is going wrong there?

Shorting the cables at the thermostat end doesn't do anything, which makes me think the cable run is open somewhere. But before I address that, I'd like to see if I can get the furnace running.
 
  #4  
Old 01-05-15, 03:15 PM
O
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Any idea why the pilot light goes out and the main burner doesn't light when I short the TH/TP and TH terminals?
 
  #5  
Old 01-05-15, 06:23 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,408
Received 1,405 Votes on 1,300 Posts
Are your connections similar to the diagram below ?

Name:  mvs.jpg
Views: 15794
Size:  41.4 KB
 
  #6  
Old 01-05-15, 07:34 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,154
Received 68 Votes on 60 Posts
PJ I believe he needs at least 560 mv at the power pile before the gas valve will open..........
 
  #7  
Old 01-05-15, 11:00 PM
O
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
yep, looks like that. yes, it does.
 
  #8  
Old 01-05-15, 11:07 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,408
Received 1,405 Votes on 1,300 Posts
There are several types of pilot generators and I believe most of these Williams units use the 340mv. one.
 
 