Rheem 90 vent issues

I have this furnace and the same problem every year when the temp drops below a certain point. The intake and outgoing vent get plugged by the moisture freezing in the pipes. I think it is the out pipe that gets plugged by frost buildup. The CO2 can't get out so the sensor shuts the furnace down because it can't vent.
 
  #2  
Old 01-06-15, 12:50 PM
A
Member
Thread Starter
Join Date: Jan 2015
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Rheem 90

Any good solutions to the exhaust vent pipe clogging every time the outside temp goes near zero?
 
  #3  
Old 01-06-15, 05:09 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Make sure the vent pipes slope upward from the furnace to the vent termination at a rate of AT LEAST 1/4" rise per foot of run. Also the pipe(s) must be supported in a manner which will prevent sagging & thus low spots.
When supporting the pipe(s), DO NOT use plastic plumbers pipe strap. It will stretch over time. Use only metal supports.
 
 