Vent question for a wall mounted heater ?

I'm look to install a 25,000 BTU (gas) wall mounted heater in my house just like this one:

Monterey 25,000 BTU/Hr Top-Vent Gravity Wall Furnace Natural Gas with Wall or Cabinet-Mounted Thermostat-2509622A - The Home Depot

According to the manual, the heater should be vented through the attic and out through of the roof.

My question is, does the vent line have to be a straight shot from the top of the heater to my roof or can i install a duct that bends and connects to an existing, unused vent on my roof?

If it's the latter, then it would save me a lot of hassle of having to cut into my room and install a new vent.

Thanks!
 
  #2  
Old 01-11-15, 04:41 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,600
Received 156 Likes on 142 Posts
If I am looking at the correct model of heater,it can only be vented out the back of the unit.
I could be wrong.
Geo
 
  #3  
Old 01-11-15, 06:03 PM
M
Member
Join Date: Dec 2004
Location: San Jose,Ca
Posts: 1,573
Likes: 0
Received 3 Likes on 3 Posts
It is top vented. If memory serves me you must have at least two feet of vent pipe off the furnace before any offset can be made. Of course you must refer to mfg instructions
 
  #4  
Old 01-11-15, 07:07 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,401
Received 38 Likes on 36 Posts
I believe this is the installation manual for the furnace you are talking about:
http://www.homedepot.com/catalog/pdf...0ce79da302.pdf

See page 14 for venting. mbk3's memory is correct. No offsets within the first 2 feet of vent.
 
  #5  
Old 01-12-15, 05:27 PM
D
Member
Thread Starter
Join Date: Jan 2015
Posts: 2
Likes: 0
Received 0 Likes on 0 Posts
Thanks guys, that's the page I was looking for. Looks like I have to wait 2ft above the header and make sure the offset is no greater tha 45 degrees from straight up.
 
  #6  
Old 01-12-15, 09:04 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,183
Received 77 Likes on 69 Posts
or can i install a duct that bends and connects to an existing, unused vent on my roof?
Dont know what your using but the vent needs to be double wall...

What duct are you talking about that bends?
 
  #7  
Old 01-13-15, 01:28 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 14,401
Received 38 Likes on 36 Posts
Maybe this kind of flexible stuff? http://www.novaflex.com/information_...fo%20Sheet.pdf
 
  #8  
Old 01-13-15, 03:17 PM
M
Member
Join Date: Dec 2004
Location: San Jose,Ca
Posts: 1,573
Likes: 0
Received 3 Likes on 3 Posts
I don't think that qualifies, I believe it must be type "B" all the way
 
 