2 zone setup on Trance XE80 for 1st floor and basement ?

Reply

  #1  
Old 02-18-15, 05:50 AM
Member
Thread Starter
Join Date: Jan 2015
Posts: 6
2 zone setup on Trance XE80 for 1st floor and basement ?

Im planning to install a 2 zone setup for my basement and 1st floor.

I have 6 ducts opening to basement and 6 opening to 1st floor

do i need to buy 6 electronic dampers or 12 electronic dampers ?
trying to keep the costs low since these things are EXPENSIVE

Can you give me some guidance please.

thanks in advance.
 
Sponsored Links
  #2  
Old 02-20-15, 07:27 AM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 13,928
If you are presently running all 12 ducts off of the furnace, I believe you will have a problem trying to use only 6. Your furnace will likely get overly hot whenever only one zone is calling for heat.
 
Reply