Old ICP furnace, pressure switch code

ICP gas furnace
GUA080A012EIN

Light flashes 3 time: pressure switch stuck open. DMM reads that the switch is closed. DMM shows 24v going into the pressure switch to the blower and into and out of the high temp switch. Furnace will not heat with the pressure switch disconnected or with the wires shorted.
Pressure switch is operational, but not tested with hydrostatic pressure meter. Im thinking its the White Rodgers control module.

Ive exhausted all of my handiman ideas for trouble shooting. Any suggestions?
 
Sponsored Links
  #2  
Old 04-24-15, 03:18 PM
Member
Join Date: Nov 2012
Location: USA
Posts: 218
Received 0 Votes on 0 Posts
When I test the safety's, I put my meter leads across the pressure switch so I can see 24 volts when the switch is open, and nothing when the switch is closed. You shouldn't read anything across the pressure switch once you hear it click!
 