Trane XB80 error code 4 and no ignition, Limit switch OK!


  #1  
Old 06-06-15, 11:21 PM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
Trane XB80 error code 4 and no ignition, Limit switch OK!

Hello

I have Trane xb80 furnance blowing cold air, I opened the panel and I found the red light blinking 4 times. Everything else is working except no ignition.

I did some research and found that it's Open Limit Switch Issue. I located the temperature limit switch, tested it continuity test by the multimeter and it's working (sound peeps with the test). I couldn't find any reset buttons, so I turned off the circuit breaker and the gas, then turned them back on, same issue!

I tested the pressure limit switch and from the google'ing, I figured out that it the continuity test should fail when the furnance is off, and it was OK! I turned the furnace back on, did the same test and it peeps (so it should be OK).

Moreover, I tried to measure the voltage between the temperature switch prop and the screw, but found zero voltage.

I'm new guy in do it yourself, but I'm trying to learn. It was super expensive to pay a technician to show up starting at $150 per hr!!!

If it's easy fix, I would like to learn it...is there anyone who can help me?

Here are some photos from inside my panel to help keeping our language close.


Thank you














 
  #2  
Old 06-07-15, 05:59 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Your roll out switches have a reset button on them. Pic # 6 right and left of the burners.
 
  #3  
Old 06-07-15, 02:15 PM
G
Member
Join Date: Oct 2002
Location: Hamilton County, Ohio
Posts: 3,927
Upvotes: 0
Received 2 Upvotes on 2 Posts
Define no ignition. Does the inducer motor run? Do you see the glow from the HSI?
 
  #4  
Old 06-07-15, 02:30 PM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
@ skaggsje
There is no reset button on them, I double checked. However, the continuity test passes on both of them. Any thoughts? Thank you
 
  #5  
Old 06-07-15, 02:34 PM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
@ goldstar
no glow at all like there is nothing trying to ignite.
The inducer motor (I think the one in pic #3) is running all the time when calling for heat.

Any Thoughts? Thank you
 
  #6  
Old 06-07-15, 02:57 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Your right no reset on that furnace. Are you pulling the wires off the switches to test them?
 
  #7  
Old 06-07-15, 03:13 PM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
no should I? I tested all of them while running and when circuit breaker is off. Thank you
 
  #8  
Old 06-07-15, 03:29 PM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
I pulled the wires off these 2 switches and the temp limit switch...all are good!
 
  #9  
Old 06-07-15, 04:50 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
There should be one more safety switch in there. Trace the yellow wire marked YL/5 from the control board to see if you can find it.
 
  #10  
Old 06-07-15, 05:31 PM
G
Member
Join Date: Oct 2002
Location: Hamilton County, Ohio
Posts: 3,927
Upvotes: 0
Received 2 Upvotes on 2 Posts
If you follow the flexible plastic hose coming from the inducer blower, it will lead you to a vacuum switch.
You need to see if that switch is closing with the inducer running. If not, check for crud in the hose or the nipples where the hose attaches to the blower and vacuum switch. That switch must close before power is applied to the HSI. If it is working properly, the next step is to check for a bad HSI.
 
  #11  
Old 06-07-15, 05:34 PM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
I couldn't find any wire labeled YL5. I looked again and I found a switch with 4 wires in it (one blue one red on each side of it), but I don't know how to test this one.

Photos are below




 
  #12  
Old 06-07-15, 05:41 PM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
I tested that switch in pic #5, it fails when the inducer not working (no peep) however when the inducer is working, it peeps (which I think it should be good??). Note, I tested it with the wires on, should I remove them for the continuity testing?

Where is that HSI? and how can I make sure it's the defective peace? does it make sense ti have error code 4 with this HSI defective?

Thank you
 
  #13  
Old 06-07-15, 06:38 PM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
I tested the igniter and it gives 72 ohms reading, so I guess it should be good!! any other thoughts?

Thank you
 
  #14  
Old 06-07-15, 07:00 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
That is a transformer, not likely your problem. I think I would start to test the switches for voltage. Use the furnace chasis for ground and other probe on each side of the switches. This will be 24V.
 
  #15  
Old 06-07-15, 07:22 PM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
No voltage at all. I tested the temp limit switch and the 2 other switches. zero voltage while it's running (after calling for heat)
 
  #16  
Old 06-07-15, 07:31 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Did you reconnect the transformer? Can you post a close up pic of the wiring diagram? I want to make sure it matches mine.
 
  #17  
Old 06-07-15, 07:39 PM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes I connected it, where can I find the wiring diagram?
 
  #18  
Old 06-07-15, 07:41 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Should be on the inside of the cover.
 
  #19  
Old 06-07-15, 07:48 PM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
No wiring diagrams, my model no TDE060A936M0
 
  #20  
Old 06-07-15, 08:18 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Can't find any thing for that model. The diagram I have shows a reverse flow switch. On the control board find the 12 connecter. Trace the yellow wire to this switch.
 
  #21  
Old 06-07-15, 08:26 PM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
the 12 connector (with 3 empty slots, so there are 9 wires only) has 2 yellow wires. One goes behind the panel (can be seen at picture #1) and the other goes to the pressure switch. Is it helpful? I appreciate your help! Thanks
 
  #22  
Old 06-08-15, 04:01 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Yes that helps, trace the yellow wire that goes behind the panel. Check for voltage at that switch.
 
  #23  
Old 06-08-15, 08:50 AM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
How can I reach stuff behind the panel?
 
  #24  
Old 06-08-15, 02:39 PM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Try pulling the wire back and forth to see where it goes.
 
  #25  
Old 06-08-15, 08:46 PM
H
Member
Thread Starter
Join Date: Jun 2015
Location: United States
Posts: 14
Upvotes: 0
Received 0 Upvotes on 0 Posts
It goes somewhere behind the panel. I can't see.

I guess it's the time for a technician! got frustrated!

Anyway thank you Sir for your help! Appreciate it!
 
 