Goodman GMH95 furnace - Inducer motor continuously running


  #1  
Old 10-25-15, 01:03 PM
S
Member
Thread Starter
Join Date: Oct 2015
Location: Canada
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Goodman GMH95 furnace - Inducer motor continuously running

Hi,
My inducer motor is continuously running - even when furnace is off at thermostat.

I suspect the relay on the control board is stuck, and thus the control board needs to be replaced.
Is there something else i can check before i go down that road?

what else would cause the inducer motor to stay one that i can check?

Thanks
 
  #2  
Old 10-25-15, 01:12 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
Welcome to the forums.

I need to confirm but on many furnaces.... when a safety stat opens..... the blower(s) are locked on. This lets you know there's a problem. There should be a trouble code blinking on the control board in the blower section. See if there is a sight glass on the blower door and look in.

Goodman trouble codes....
Name:  Goodman trouble codes.JPG
Views: 5790
Size:  42.7 KB
 
  #3  
Old 10-25-15, 02:41 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
>



That's a likely cause of the problem. But use an AC voltmeter to check to see if you have 24 VAC on the W terminal. Any time you have 24 VAC there, the inducer motor will run. That could be caused by a thermostat that is staying on.
 
  #4  
Old 10-25-15, 05:09 PM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 2,665
Received 235 Upvotes on 208 Posts
Most hot air furnaces have a temperature sensor that has a contact (temperature selectable) that keeps the fan motor powered after the burner goes off (thermostat satisfied) to remove the residual heat until the decreasing temperature opens the contact removing power from the fan motor. This temperature sensor operates by rotating in response to temperature changes. A cam on the rotating member operates the contact in the fan control circuit.
The temperature sensor is a mechanical device that sometimes gets stuck and will unstick with a tap to the sensor. The sensor is usually located on the burner side of the furnace near the top. The furnace cover must be removed to gain access to tap the sensor.
 
  #5  
Old 10-25-15, 05:35 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
Bz..... that control you are describing would affect the main blower fan.
In this case the OP's draft inducer is staying energized.


SP... normally.... when there is power on the W terminal you would get heat.... not just the draft inducer running. The problem here is a defective relay or open safety.
 
  #6  
Old 10-26-15, 10:41 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 2,665
Received 235 Upvotes on 208 Posts
I agree my solution was for a different problem.
 
  #7  
Old 10-27-15, 04:38 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
>


Normally, yes. But we are dealing with a furnace that isn't working normally.

Checking to see what the thermostat is doing by measuring the voltage at the W terminal is just being thorough and eliminating possible problems, in my view.
 
  #8  
Old 10-27-15, 09:29 PM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 1,799
Received 52 Upvotes on 46 Posts
disconnect w completely, tape it off, restart and see what happens.

on some furnaces the inducer may start running if there's a flame sensed when no call for heat error; could be caused by an issue in the board or a maybe even a tiny short to ground in the flame sensing circuit.
 
 