Furnace won't ignite

I have a Heil gas furnace model: NUGE075BG01

When heat is called for from the thermostat the inducer blower runs but the spark ignitor never clicks. The inducer blower just continues to run. Any ideas as to where to start troubleshooting? I have changed the filter and checked that the exhaust has no obstructions.

Thanks!
 
Sponsored Links
  #2  
Old 09-27-16, 11:11 AM
Member
Join Date: Oct 2002
Location: Hamilton County, Ohio
Posts: 4,296
Received 2 Votes on 2 Posts
First place to check is at the vent pressure switch. There is a tube from the inducer motor to the switch. Check that the tube and attachment nipples do not have any water or debris in them.

If you have an ohm meter, check the switch wire leads. The switch should go from open with the inducer off, to closed with the inducer running. If not closed, gas flow and ignition will not occur.
 
  #3  
Old 09-27-16, 12:53 PM
Member
Thread Starter
Join Date: Jul 2013
Location: USA
Posts: 10
Received 0 Votes on 0 Posts
Thanks, I will give that a look this afternoon.
 
  #4  
Old 09-27-16, 04:54 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,582
Received 416 Votes on 389 Posts
See if there is a clear window in the blower door. Your furnace should have a control board down in the blower section. It should have a blinking LED on it for a trouble code.

You can open the blower door to look for a board but when the door is opened..... the furnace is dead. There should be a list of trouble codes listed on the back of the door that will guide you.

Reclose the door..... fire up the furnace and watch for codes.
 
  #5  
Old 09-28-16, 01:04 PM
Member
Thread Starter
Join Date: Jul 2013
Location: USA
Posts: 10
Received 0 Votes on 0 Posts
Thanks for all the input guys! I ended up taking some of the venting apart to check for blockage and discovered a dead bird restricting the airflow! I removed it and the furnace is running beautifully. I've never been more excited to find a dead bird!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: