Rheem blowing cold air

Hello, I just purchased a home with a HVAC unit installed in the attic that is 4 years old. Last night was the first time I've attempted to use the heat and it only blows cold air. Upon further inspection i find the burners are not burning at all. It is a conventional unit with A/C and only 5 wires going to the thermostat (W, Y, G, R and blue (C)).

I have tried connecting red & white wire together to rule out the thermostat.

I have tried to turn off the 15amp breaker and turn it back on.

Fan on thermostat is set to auto, heat set 10 degrees higher than room temp

When I take the door off I can see it is electric ignitor, I will post a picture.

Unit it a rheem brand. Natural gas. I have checked the 3 valves in the gas line (including the two on the contraption where gas comes in from the street) - all are open position.

When heat is turned on I hear a little whine noise then the blower turns on. I tried dimming the light and I don't think I see a spark or anything.

What else should I check?
Thank you!
 
  #2  
Old 10-11-16, 10:46 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
Welcome to the forums.

Remove the lower blower cover. Read the back of the door for trouble codes.
Locate the control board in the blower area.

While the blower cover is off the furnace has no power. Hold in the door safety switch or put the cover back on and look thru the sight glass for the blinking LED. Allow it to try to fire and count the flashes.
 
  #3  
Old 10-11-16, 10:54 AM
D
Member
Thread Starter
Join Date: Oct 2016
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
Cool beans, thanks! I'll give that a try
 
  #4  
Old 10-11-16, 11:08 AM
D
Member
Thread Starter
Join Date: Oct 2016
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
Here's the 2 pictures... I did the light check - and got 3 blinks from the green light in the middle. I was unable to find a glossary or what that means...Name:  IMG_0337.jpg
Views: 3694
Size:  50.0 KB Name:  IMG_0341.jpg
Views: 2802
Size:  50.1 KB
 
  #5  
Old 10-11-16, 11:13 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
The codes are on the back of one of the service panels. Usually the blower one.

Preliminary..... Rheem three flash code signifies open safety sensor. Possibly a heat sensor near the burner/flue area. The switches are oval in shape. You're looking for one with a tiny red reset button on it.

You may need to post the model number off the ID plate.
 
  #6  
Old 10-11-16, 11:41 AM
D
Member
Thread Starter
Join Date: Oct 2016
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
There were some labels on the back of each panel, but nothing to do with flashes. Might have to look closer. Here's another pic I took of some identifying material. Name:  IMG_0340.jpg
Views: 2500
Size:  22.5 KB
 
  #7  
Old 10-11-16, 01:55 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
No help. Post the model number off the ID tag on the sidewall near the burner.
 
  #8  
Old 10-17-16, 06:53 AM
D
Member
Thread Starter
Join Date: Oct 2016
Posts: 10
Upvotes: 0
Received 0 Upvotes on 0 Posts
Wanted to let you all know I called a professional and turns out there was water in the piping where the burners blow the flames/hot air. The A/C is blowing it's humid air through the furnace in the summer time probably causing the condensation. Whoever installed this unit did it in reverse so the professional recommends I have it fixed or else I may have to do this every year and maybe the furnace will rust out? Bummer. Also learned they never bonded/grounded the yellow flex gas line and the condensate line runs into the main stack ruining my dry vent. Oh the joys of home ownership... No idea why none of this was picked up on the inspection.
 
  #9  
Old 10-17-16, 11:27 AM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
>



Sounds like you had a VERY good repairman!

That sounds like a bunch of quite subtle problems. Home inspectors have only a basic knowledge of HVAC systems. Usually if they think they see a problem, they will recommend an inspection by a capable repairman.

Even a capable repairman might have missed some of the things you mention, absent an actual problem that needed to be diagnosed. That is to say, I might have missed some of that!
 
 