Goodman furnace won't turn on
replaced IFC cleaned out inducer after getting code for 3 blinking light and 4 blinking light now I have a solid light I can hear the click from control board but nothing happens is there a DIY solution for this
#2
Member
First, can we have some information of what furnace it is? And what 3 and 4 blinks mean? Is there a schematic that shows what a solid light indicates?
#3
Take the cover off the burner compartment of the furnace.
Carefully observe the sequence of events which occur when you turn up the thermostat, and post that sequence here, in order and in detail.
Carefully observe the sequence of events which occur when you turn up the thermostat, and post that sequence here, in order and in detail.
#6
Member
Thread Starter
Join Date: Nov 2016
Location: USA
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
furnace won't turn on
I have a Goodman model GMT090-4 solid light means normal operation 3 blinks pressure switch failure to close 4 blinks open limit switch both 3 and 4 codes have come up first 3 I cleaned out the inducer port it worked then it shut down then it started blinking code 4 but kept working fine then it shut down with a solid light no sequence at all I left the power on for a few hours went back to check on it its blinking 3 times again

#7
Member
If you cleaned out the small port where the hose connects to the inducer trap, I would next check for an obstruction in the vent pipe from the inducer to the outside.