Troubleshooting Code 33 on Carrier 59SC2B


  #1  
Old 11-22-16, 04:49 PM
R
Member
Thread Starter
Join Date: Dec 2015
Posts: 25
Upvotes: 0
Received 0 Upvotes on 0 Posts
Exclamation Troubleshooting Code 33 on Carrier 59SC2B

I am back with a similar problem I faced about a year ago (wonder if it's going to be an annual event ). Last time I used to see code 33 followed by 13. The service confirmed a defective blower motor as folks here had indicated and replaced it. The problem went away.

Few days ago, Nest reported that the furnace was stopping frequently and I noticed code 33 again. Only this time there was no code 13 and it seemed to recover after 4 minutes. Here is what I see today -

- Furnace turns on
- After about 15 seconds, the blower turns on
- Both continue to run for 4 minutes
- Code 33 starts flashing and the furnace stops
- Blower continues to run for another 4 minutes and then stops
- The light becomes steady
- Another 10-15 seconds, the furnace turns on and continues with the above cycle

For code 33 (Limit or Flame Rollout switch is open), here is what I have done so far -

1. Defective blower motor or capacitor - there doesn't seem to be any issue with the blower this time. No noise while starting, no burning smell and seems to run smoothly
2. Dirty filter / restricted dirt system - I replaced the 20x20 filter even though it was replaced a month ago and wasn't dirty at all. Also, ensured all registers are open and flowing air when the blower runs. Didn't help. Wonder if I should run the system for 4 minutes without any filter and see if it still stops.
3. Loose blower wheel - there is absolutely no unusual noise when the blower runs so this seems unlikely
4. Defective switch or connection - This could be a problem. How do I verify this? I couldn't locate a red button inside the burner compartment
5. Inadequate combustion air supply (flame rollout switch or fuse link open) - Is there a way I could check this as well?
6. Open flame rollout switch or fuse link. Manual reset or replace - I'd like to replace and see if that helps (this seems to be the easiest and most economical option)

Seems like #4-6 are more likely. What would you have me try? Thanks for any guidance.
 
  #2  
Old 11-22-16, 04:54 PM
R
Member
Join Date: Oct 2016
Posts: 2,135
Received 185 Upvotes on 169 Posts
Do you have a meter? You need to see which switch is open.
 
  #3  
Old 11-22-16, 05:17 PM
R
Member
Thread Starter
Join Date: Dec 2015
Posts: 25
Upvotes: 0
Received 0 Upvotes on 0 Posts
I do - which switch should I start with? Here is the burner compartment -

 
  #4  
Old 11-22-16, 05:34 PM
R
Member
Thread Starter
Join Date: Dec 2015
Posts: 25
Upvotes: 0
Received 0 Upvotes on 0 Posts
I see one switch (set to ON) -


Or, are you talking about these?

 
  #5  
Old 11-22-16, 06:10 PM
R
Member
Join Date: Oct 2016
Posts: 2,135
Received 185 Upvotes on 169 Posts
No, you need to check the limit and rollout.
 
  #6  
Old 11-22-16, 06:16 PM
R
Member
Thread Starter
Join Date: Dec 2015
Posts: 25
Upvotes: 0
Received 0 Upvotes on 0 Posts

Are they in this picture? Let me google a bit.
 
  #7  
Old 11-22-16, 07:00 PM
R
Member
Thread Starter
Join Date: Dec 2015
Posts: 25
Upvotes: 0
Received 0 Upvotes on 0 Posts
I think this is the one? Checked this - shows closed (0.0 ohm) -


Wonder what this is but shows closed -
 
  #8  
Old 11-22-16, 07:04 PM
R
Member
Thread Starter
Join Date: Dec 2015
Posts: 25
Upvotes: 0
Received 0 Upvotes on 0 Posts
I tried resetting after turning power to the furnace off (pressing the red dot) and then turning the furnace off. The light started flashing code 33 again and after 4 minutes furnace and blower both started again and ran for 4 minutes.

If it's a switch, it precisely opens after 4 minutes and then closes after another 4. Shouldn't be heat related as I tried it this time with the burner compartment open so heat build-up should have taken longer than 4 minutes.
 
  #9  
Old 11-23-16, 01:50 PM
R
Member
Thread Starter
Join Date: Dec 2015
Posts: 25
Upvotes: 0
Received 0 Upvotes on 0 Posts
Anything else should I try folks?
 
  #10  
Old 11-23-16, 02:36 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
http://www.doityourself.com/forum/ga...s-furnace.html

Read through the thread above. Your are both trying to identify a problem.

But make any reply on this thread so as not to sow confusion.
 
  #11  
Old 11-23-16, 03:45 PM
R
Member
Thread Starter
Join Date: Dec 2015
Posts: 25
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks SeattlePioneer. Yes, the problem seems similar. I haven't tried running the furnace for more than 15-20 minutes (2-3 cycles of 4 minutes) at a time so never had to recycle power like Neil needs to after about 40 minutes.

I'll try running for 30+ minutes tonight after removing both the filters to see if it's really the air filters.
 
  #12  
Old 11-23-16, 04:16 PM
R
Member
Thread Starter
Join Date: Dec 2015
Posts: 25
Upvotes: 0
Received 0 Upvotes on 0 Posts
Reading from the other thread, I wonder if I am looking at the right manual. Model number from the burner door is 59SC2B080S211120 I am looking at this. Odd that the PDF itself doesn't list any model information. My installation is horizontal though.
 
  #13  
Old 11-23-16, 05:53 PM
R
Member
Thread Starter
Join Date: Dec 2015
Posts: 25
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ran for about 90 minutes and it didn't need any power recycle. But it stopped every few minutes so it's not really a constant run like Neil's.

The continuous runtime wasn't constant - one time it ran for almost 6 minutes without stopping and other times between 4 and 5 minutes. I had removed both the filters so that might have to do with longer runtime but since it didn't eliminate the stop, can I now rule out that dirty filter or registers causing it?
 
 