Ruud not staying lit I cleaned flame sensor still shutting down


  #1  
Old 11-28-16, 08:32 AM
B
Member
Thread Starter
Join Date: Nov 2016
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ruud not staying lit I cleaned flame sensor still shutting down

I have a 1992 ruud ugdg-10ebrjr, I turned on for first time this season. Blowers come on ignitor glows gas blows blue for 5 second then she shuts down. I cleaned flame sensor with same results. Should I just buy a new sensor first? The circuit board was replaced over the summer maybe i missed something there. I will upload some pics if i can.Name:  20161128_074122.jpg
Views: 19609
Size:  36.0 KBName:  20161128_074148.jpg
Views: 17732
Size:  47.0 KBName:  20161128_074116.jpg
Views: 17087
Size:  28.6 KB
 
  #2  
Old 11-28-16, 08:46 AM
R
Member
Join Date: Oct 2016
Posts: 2,137
Received 185 Upvotes on 169 Posts
You can use a meter to measure ma from the flame sensor.
I see some rust and signs of water damage. Heat exchanger ok in that unit?
 
  #3  
Old 11-28-16, 08:53 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
Welcome to the forums.

Is that rust all over the burners..... they sure don't look in good shape ?
Is that a before or after picture.... the flame rod doesn't look clean ?
Are all the burners lighting immediately on supply of gas ?

The flame creates a conductive path from the sensor rod to ground. Burner grounds as well control board grounds are critical for proper operation. Make sure the screws in the control box are clean and getting ground to the control.

That module has a flame LED on it...... what is it doing during burner operation ?

Name:  20161128_074122.jpg
Views: 14753
Size:  29.2 KB
 
  #4  
Old 11-28-16, 09:33 AM
B
Member
Thread Starter
Join Date: Nov 2016
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
I have a mutimeter how do i test the flame sensor?
 
  #5  
Old 11-28-16, 09:39 AM
B
Member
Thread Starter
Join Date: Nov 2016
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you for response. The flame sensor is bright and shiny now. The board itself is not grounded as far as I can tell. Does the ground for flame sensor come from the sheet metal screw securing it?

All the burners fire blue immediately as soon as I hear it click then flames out after 5 seconds. The yellow flame LED blinks very faint(can hardly tell) after flame out.
 
  #6  
Old 11-28-16, 09:50 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
The flame sensor LED should be locked on bright....not flickering when flame is present.

The control box is usually on a metal frame that get mounted to the furnace body.

The flame sense path is.... AC signal leaves the control box on the flame sense wire. Gets applied to the flame sensor rod. Gets rectified into DC via the flame. Then there is current flow from the flame to the metal ground which needs to be the same metal ground as the control box. The screw on the rod just holds it in place. It's a non functioning part.
 
  #7  
Old 11-28-16, 10:10 AM
B
Member
Thread Starter
Join Date: Nov 2016
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
Name:  20161128_074127.jpg
Views: 15759
Size:  40.2 KB

Here is a pic of control box, the back of box is plastic. I do not see a ground wire or mounting screw that grounds the board.
 
  #8  
Old 11-28-16, 01:11 PM
B
Member
Thread Starter
Join Date: Nov 2016
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
Is there a way to "jump" or bypass the flame sensor to rule out?
 
  #9  
Old 11-28-16, 03:07 PM
R
Member
Join Date: Oct 2016
Posts: 2,137
Received 185 Upvotes on 169 Posts
No, you need to get a meter capable of measuring the signal from the flame sensor and go from there.
Bypassing safety controls, even when possible, doesn't prove anything. Use meters and instrumentation to troubleshoot properly.
 
  #10  
Old 11-28-16, 03:22 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
Ok

No.... you can't jump out the flame sensor. It IS your problem. The LED is telling you that.
It's probably not the rod... it's the path.

What is the model number on that board ?
A solid ground to the control board is a must.
 
  #11  
Old 11-28-16, 05:07 PM
B
Member
Thread Starter
Join Date: Nov 2016
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
part number

The board part number is 62-24084-82. Where should I ground the board?

I have a muti-meter just not sure how to test flame sensor.
 
  #12  
Old 11-28-16, 06:23 PM
B
Member
Thread Starter
Join Date: Nov 2016
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
I do not see any ground on the board. Where should i run a direct ground on the board?
 
  #13  
Old 11-28-16, 06:29 PM
B
Member
Thread Starter
Join Date: Nov 2016
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
Name:  20161128_192437.jpg
Views: 14656
Size:  46.8 KBName:  20161128_192447.jpg
Views: 14636
Size:  49.3 KB

Hete are some more pictures of the board
 
  #14  
Old 11-28-16, 07:28 PM
B
Member
Thread Starter
Join Date: Nov 2016
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
this may be the problem

https://arnoldservice.com/product/62...me-sensor-kit/

62-24044-71 Ruud Rheem Furnace Remote Flame Sensor Kit


If your furnace was made before March 2, 1994, and if you replacing the 62-24084-82 furnace control board, upgrade your flame sensor with 62-24044-71 Ruud Rheem Furnace Remote Flame Sensor Kit.


I replaced the board in june this year, according to this site the sensor needs to be changed. It look the same to me.
 
  #15  
Old 11-28-16, 07:57 PM
SeattlePioneer's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Jul 2007
Location: Seattle, Wa
Posts: 4,469
Upvotes: 0
Received 1 Upvote on 1 Post
Actually, you can bypass the flame sensor.

the flame sensor is just a way of exposing the voltage on the flame sensor wire to the furnace burner flames.

So you can connect the flame sensor wire to a screwdriver and put the screwdriver into the flames.

Probably not going to tell you much though, since you've already cleaned the flame sensor.

Try measuring the AC voltage being applied to the flame sensor during the ignition cycle ----it should be 24 VAC in most cases. If you get zero volts, you probably have a bad circuit board.
 
  #16  
Old 11-28-16, 08:31 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
OP just changed the board recently.

I looked into the flame rod kit. It looks like more rod is in the flame with the new version.
I don't know if you have to upgrade to it or if yours is ok. Your rod seems to be pretty well in the flame path.

The diagram shows where the new one would sit.

Name:  rod.JPG
Views: 14663
Size:  33.1 KB

You could try a temporary jumper from the C terminal to any shiny metal part and see if that improves the signal.
 
  #17  
Old 11-28-16, 09:09 PM
B
Member
Thread Starter
Join Date: Nov 2016
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks where would i locate the C terminal
 
  #18  
Old 11-29-16, 05:09 AM
B
Member
Thread Starter
Join Date: Nov 2016
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
So run a jumper from c terminal in pic to the ground to rule out if sensor it bad?I ran a jumper from C screw in pic to a shiney surface with same result. I also tried taking the sensor out and held it deeper in the flame and still shuts down


Name:  20161129_060643.jpg
Views: 14541
Size:  47.2 KB
 

Last edited by bigdog100; 11-29-16 at 05:37 AM.
  #19  
Old 11-29-16, 09:25 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
At this point the only thing left to do is to check the flame sense circuit.
Setting your meter to the AC volts scale.... either auto or next step over 24vac.... and measure from the flame sense wire to ground. No call for heat needed for this test.

The other test is a little trickier. You would need a microamp scale on your meter. You would disconnect the flame rod and connect one meter lead to the removed wire and the other lead to the flame rod. You should be measuring something around 4-6ua when the burner fires.
 
  #20  
Old 11-29-16, 06:33 PM
B
Member
Thread Starter
Join Date: Nov 2016
Posts: 12
Upvotes: 0
Received 0 Upvotes on 0 Posts
problem solved

OK, the problem was fixed by much research. The new board did require the Protech Rheem Ruud 62-24044-71 Remote Flame sensor Rod kit. Thank you for the troubleshooting. If anyone else runs into this issue hope this helps.
 
 