Advice regarding zone malfunction
#1
Member
Thread Starter
Join Date: Jan 2017
Location: United States
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Advice regarding zone malfunction
We have natural gas forced hot air heat. Our heat professional added a zone so that we could heat one room in the basement using the furnace that heats the main floor of the house. He added zone 2 for the basement that opens a vent that fills a small duct for that room off of the main duct. When the basement thermostat triggers the furnace, the furnace heats the basement as well as the main floor.
We can live with that... the problem I am experiencing is that for some reason now when the main floor thermostat triggers the heat, heat is now coming through the basement vent as well. I'm thinking that either the vent that channels heat to the basement is stuck open, or there is something wrong with the honeywell "controller" (forgive me, I don't know heating terminology).
When the upstairs thermostat is triggered and the downstairs one is not, I see this on the controller:
Heat: Red
Heat: no color
Zone 1: Green
Zone 2: Red
Zone 3: Red (this zone is actually unwired)
When the thermostat turns the heat off, "Heat" turns to No Color and Purge turns yellow, followed by a resting state of
Heat: no color
Heat: no color
Zone 1: Green
Zone 2: Green
Zone 3: Green
Can anyone help me to debug this?
We can live with that... the problem I am experiencing is that for some reason now when the main floor thermostat triggers the heat, heat is now coming through the basement vent as well. I'm thinking that either the vent that channels heat to the basement is stuck open, or there is something wrong with the honeywell "controller" (forgive me, I don't know heating terminology).
When the upstairs thermostat is triggered and the downstairs one is not, I see this on the controller:
Heat: Red
Heat: no color
Zone 1: Green
Zone 2: Red
Zone 3: Red (this zone is actually unwired)
When the thermostat turns the heat off, "Heat" turns to No Color and Purge turns yellow, followed by a resting state of
Heat: no color
Heat: no color
Zone 1: Green
Zone 2: Green
Zone 3: Green
Can anyone help me to debug this?
#2
The basement damper linkage needs to be adjusted ( it isn't fully closed when it should be) or the operation of the basement damper must be reversed .
It sounds like you have a Honeywell zone control.
Do you have a Honeywell damper serving the basement?
Does the damper have red and green LED's indicating position (or a giant arrow)?
The red tab can be used to limit the ability to closed the damper.
It sounds like you have a Honeywell zone control.
Do you have a Honeywell damper serving the basement?
Does the damper have red and green LED's indicating position (or a giant arrow)?
The red tab can be used to limit the ability to closed the damper.
#3
Member
Thread Starter
Join Date: Jan 2017
Location: United States
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It is a honeywell (I'll attach the pictures I took of the states I mentioned).
I haven't actually seen the basement damper linkage - it's under insulation.
I haven't actually seen the basement damper linkage - it's under insulation.
#4
I see that zone 1 doesn't have a damper. If it did you would probably end up with lockouts.
If the Zone 2 damper is a Honeywell with the factory configuration it is wired incorrectly. M1 and M6 should connect to the damper wires. It looks like you have M1 and M4 in use.
If the Zone 2 damper is a Honeywell with the factory configuration it is wired incorrectly. M1 and M6 should connect to the damper wires. It looks like you have M1 and M4 in use.