Goodman Quit, High Limit Open
#1
Member
Thread Starter
Join Date: Jan 2017
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Goodman Quit, High Limit Open
Happy winter, lucky it is not too cold here in NC this week and we have a nice gas fireplace that heats the house. I have a 6 year old Goodman MVC95 furnace mounted in the crawl space horizontally. Last week was a very cold week and the unit worked perfect as far as I can tell. When I saw the E3 code I checked the filters which were dirty and changed them then I checked the condensate system which is all open and running free. The intake and vent for the unit are free of junk. So then I tested continuity of the limit switches, one auto in the body was closed and the 2 on the burner rack were manual reset and they are closed. I then checked the pressure switches and the flame sensor all good. I turned the unit back on to see if it would start up it went into OP mode the draft blower came on for a few seconds then it quit and the E3 code came back on.
Help
Help
#2
Member
Pull the 15 pin connecter off the board and check continuity on pin #1 orange and pin #10 pink.
#4
Not concerned with continuity on the board. You need to check all the limits in the colored loop. They must all show continuity.

#5
Member
Thread Starter
Join Date: Jan 2017
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
So I pull the connectors on a powered down unit and check continuity between the terminals? Just want to do this right. I have 5 limits to test correct?
Last edited by Matt Rogers; 01-16-17 at 11:47 AM. Reason: confused