Goodman Quit, High Limit Open

Happy winter, lucky it is not too cold here in NC this week and we have a nice gas fireplace that heats the house. I have a 6 year old Goodman MVC95 furnace mounted in the crawl space horizontally. Last week was a very cold week and the unit worked perfect as far as I can tell. When I saw the E3 code I checked the filters which were dirty and changed them then I checked the condensate system which is all open and running free. The intake and vent for the unit are free of junk. So then I tested continuity of the limit switches, one auto in the body was closed and the 2 on the burner rack were manual reset and they are closed. I then checked the pressure switches and the flame sensor all good. I turned the unit back on to see if it would start up it went into OP mode the draft blower came on for a few seconds then it quit and the E3 code came back on.

Help
 
  #2  
Old 01-16-17, 09:59 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Pull the 15 pin connecter off the board and check continuity on pin #1 orange and pin #10 pink.
 
  #3  
Old 01-16-17, 10:59 AM
M
Member
Thread Starter
Join Date: Jan 2017
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
Checked no continuity on the board or in the connector
 
  #4  
Old 01-16-17, 11:10 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
Not concerned with continuity on the board. You need to check all the limits in the colored loop. They must all show continuity.

Name:  mvc95.jpg
Views: 1338
Size:  50.1 KB
 
  #5  
Old 01-16-17, 11:35 AM
M
Member
Thread Starter
Join Date: Jan 2017
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
So I pull the connectors on a powered down unit and check continuity between the terminals? Just want to do this right. I have 5 limits to test correct?
 

Last edited by Matt Rogers; 01-16-17 at 11:47 AM. Reason: confused
  #6  
Old 01-16-17, 12:12 PM
M
Member
Thread Starter
Join Date: Jan 2017
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
found a limit on top of the blower that was tripped, I reset it and the unit came on. I guess the dirty filter overheated the fan and the limit cut in.
 
  #7  
Old 01-16-17, 01:04 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,091
Received 3,423 Upvotes on 3,069 Posts
Definitely overheated. Good job.
Most are auto reset..... that one wasn't.
 
  #8  
Old 01-16-17, 07:55 PM
M
Member
Thread Starter
Join Date: Jan 2017
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks so much I am a remodeling contractor so I like to do things myself, your help was great.
 
  #9  
Old 01-17-17, 09:34 AM
M
Member
Thread Starter
Join Date: Jan 2017
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
Dam the limit popped again. Its the limit on the blower housing
 
  #10  
Old 01-17-17, 09:41 AM
R
Member
Join Date: Oct 2016
Posts: 2,137
Received 185 Upvotes on 169 Posts
Time to start doing some diagnosing to see why. What's the heat rise?
 
  #11  
Old 01-17-17, 11:55 AM
M
Member
Thread Starter
Join Date: Jan 2017
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
I'm testing the blower it seems to have quit
 
  #12  
Old 01-17-17, 01:08 PM
M
Member
Thread Starter
Join Date: Jan 2017
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
new wrinkle, I tried to run the fan only mode no love just a F7 code and 69 code
 
  #13  
Old 01-17-17, 02:00 PM
M
Member
Thread Starter
Join Date: Jan 2017
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
F7 as I found out is fan on continuous. I am going to test the capacitor and resistance on the motor windings for the different speeds.
 
 