Model of the furnace: Keeprite high efficiency gas furnace
Thermostat: Honeywell 4110 PRO
Thermostat wiring: 4 wires [No C wire]
Heating and cooling: yes
I bought a new house and the furnace is one year old. Due to renovations, no one lived here so not sure it has been used. temperatures fell and I started using heating. Below are the events that follow:
Troubleshooting steps already done:
Before calling the HVAC technician and paying him $100, I want to know where could be there problem?
Any more troubleshooting steps will be highly appreciated. I just want to isolate the problem.
Thanks
Thermostat: Honeywell 4110 PRO
Thermostat wiring: 4 wires [No C wire]
Heating and cooling: yes
I bought a new house and the furnace is one year old. Due to renovations, no one lived here so not sure it has been used. temperatures fell and I started using heating. Below are the events that follow:
- Heat call is made at thermostat and I can hear the condensate fan starting
- After a min or so, the burners kick in. I can see the blue flames running for about 2-3 mins
- Sometimes the blower kicks in and sometimes it doesn't. [This is the key problem]
- If the blower kicks in, the heating is normal until cut-off temp, when the entire furnace shuts down
- If the blower doesn't kick in, the burners are shut down with fault code 4 which turns to 7 and the loop starts again [The KeepRite fault codes are here: http://tradesmandrcool.com/wp-conten...TEHighEff.pdf]
Troubleshooting steps already done:
- Vents and filter: checked. No blocks
- Piping: checked. No blocks
- Reset switches: tried
- Blower squirrel cage rotation by hand: free to rotate
- When the blower runs, no noise or humming sound is there
- Thermostat wiring: checked
- Few days ago, the blower did not kick in at all. I Shut down the entire furnace and started the next day -> it worked but today its giving the intermittent runs again
- Condensate drainage: great
Before calling the HVAC technician and paying him $100, I want to know where could be there problem?
Any more troubleshooting steps will be highly appreciated. I just want to isolate the problem.
Thanks
#2
Member
Possible a loose connection. Check all wire terminations between the blower motor and the power relay for tight connections. If the motor is multiple speeds, try a different speed by moving the power wire . Terminations for different speeds are usually marked HIGH, MED and LO at the motor or near the power relay. Hope this helps.
#4
Welcome to the forums.
I'm not familiar with Keep Rite products and it appears they were bought by ICP. There will be a model number for your furnace on the inside wall near the burner on an ID plate.
There should be a capacitor attached to your blower motor and that's where I would normally start but they don't usually go bad in a year..... or on a one year old furnace.
Have you tried putting the thermostat into FAN ON mode ?
I'm not familiar with Keep Rite products and it appears they were bought by ICP. There will be a model number for your furnace on the inside wall near the burner on an ID plate.
There should be a capacitor attached to your blower motor and that's where I would normally start but they don't usually go bad in a year..... or on a one year old furnace.
Have you tried putting the thermostat into FAN ON mode ?