Older Rheem shutting down.

I have an older Rheem 80 plus from I think 1987. I tried to fire it up last week for the first time since spring. Put a new filter in and found out once the furnace was going for about 10 seconds the flames went out. The circuit board only has an LED with a max of 3 codes. It was blinking twice which indicated a weak flame signal. I don't have a flame sensor rod but it is an HSI unit. The HSI is about 4 years old. I put an ohm meter on it and got 158 ohms. Since pulling it out, inspecting it and reinstalling it now fires for 4 seconds and flashes 1 flash indicating ignition lockout.. only other thing I have replaced was the circuit board 2 years ago. I read the HSI should be around 40-70 ohms. Thought?
 
  #2  
Old 10-29-17, 02:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,102
Received 3,424 Upvotes on 3,070 Posts
Welcome to the forums.

Your HSI does sound like the resistance is a little high although that usually doesn't affect its flame sensing ability. The HSI does need to be fully engulfed in the flame though.
 
 