American Standard Gas Furnace


TomBurns's Avatar
Member

Join Date: Nov 2017
Posts: 10

11-13-17, 04:06 PM   #1 (permalink)  
American Standard Gas Furnace

Hi I purchased a used propane furnace. I hooked it up to test it and the chimney fan came on but not heat. While checking things I shorted the limit sw. to ground now the chimney fan wonít start. I donít see a fuse anywhere. The red light is blinking steady on the control panel. Did I possibly blow the low volt transformer?

 
Sponsored Links
roughneck77's Avatar
Member

Join Date: Oct 2016
Posts: 422

11-13-17, 04:19 PM   #2 (permalink)  
First, since you purchased used equipment, is the heat exchanger ok and safe to us in this unit? Is it converted to LP?

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,892
NJ

11-13-17, 04:42 PM   #3 (permalink)  
The red light is blinking steady on the control panel.
Blinking steady ? Blinking what steady ?

That light serves as a fault indicator. The flash codes are listed on the back of the blower door.
If the red LED is flashing.... the transformer is ok as the board runs on 24vac.

An AS furnace should be using a control board with a fuse. It is a plastic type automotive fuse somewhere between 3-5A.


~ Pete ~


Last edited by PJmax; 11-13-17 at 08:37 PM. Reason: typo
 
TomBurns's Avatar
Member

Join Date: Nov 2017
Posts: 10

11-13-17, 04:58 PM   #4 (permalink)  
Gas Furnace

Yes the red light blinks on off on off and not blinking codes. The board in my furnace does not have any fuse I can see. The furnace was used with LP prior and the heat exchanger is OK. The unit was running prior to being removed.

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,892
NJ

11-13-17, 08:40 PM   #5 (permalink)  
In order for me to help you further..... I need a model number for that furnace. It's inside on the side wall near the burner. You could post the model number off the control board too.

I would have expected a fuse to blow... if there was one. A quick short usually won't hurt the transformer. You could check the sensor you shorted. There should be 24vac on both sides of it measured to ground. Normally if the limit circuit was open..... you'd get a dedicated fault for that. A bit of a mystery here.


~ Pete ~

 
TomBurns's Avatar
Member

Join Date: Nov 2017
Posts: 10

11-14-17, 10:46 AM   #6 (permalink)  
American Standard Furnace

Furnace Model AUD140C960A1
Control Model 50A50-405

if I jump out the t-stat the chimney fan works
and I now am getting a three blink code
(Pressure Sw.)
I am getting a 27vac at both sides of the limit
sw.
Most likely when I shorted the limit sw. I burnt up the t-star?
There is three wires on the pressure sw two yellow have 27vac and no voltage at the orange wire with the fan running. Hope this helps. Thanks

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,892
NJ

11-14-17, 11:24 AM   #7 (permalink)  
The pressure switch won't close without the proper vacuum on it. That requires the proper flue connected to the furnace. On a call for heat..... just as the draft inducer starts..... you can short the pressure switch and see if the furnace continues with the ignition cycle.


~ Pete ~

 
TomBurns's Avatar
Member

Join Date: Nov 2017
Posts: 10

11-14-17, 11:39 AM   #8 (permalink)  
American Standard Furnace

Add info.
I checked the pressure sw with an ohm meter and itís working ok but I have no vacuum at the hose at all.
I put a wire through the hose into the fan plentym but still no vacuum?

 
TomBurns's Avatar
Member

Join Date: Nov 2017
Posts: 10

11-14-17, 11:44 AM   #9 (permalink)  
Yes it will continue and the ign. glow l comes on but propane valve is not opening. I currently have it hooked up to a propane tank with a gas grill regular to test unit prior paying to have it installed?

 
TomBurns's Avatar
Member

Join Date: Nov 2017
Posts: 10

11-14-17, 12:06 PM   #10 (permalink)  
American Standard

the valve did open and gas valves lit off but week orange flame for a few seconds and they go off, Iím sure the regulator is not enough.

 
TomBurns's Avatar
Member

Join Date: Nov 2017
Posts: 10

11-14-17, 01:42 PM   #11 (permalink)  
American Standard furnace

I did put a T exhaust pipe on the exhaust with a barometric vent, would it need more to create the needed pressure to create the proper vacuum for the pressure sw?

 
TomBurns's Avatar
Member

Join Date: Nov 2017
Posts: 10

11-14-17, 04:15 PM   #12 (permalink)  
The fan was missing half of the blades.

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,892
NJ

11-14-17, 04:46 PM   #13 (permalink)  
This sounds like a purchase to pass on.


~ Pete ~

 
roughneck77's Avatar
Member

Join Date: Oct 2016
Posts: 422

11-14-17, 07:40 PM   #14 (permalink)  
The inducer fan is missing blades?
I’d pass on this furnace.

 
TomBurns's Avatar
Member

Join Date: Nov 2017
Posts: 10

11-15-17, 05:05 PM   #15 (permalink)  
American Standard Furnace

So if anyone has a bad fan on their inducer motor should get a new furnace?

 
roughneck77's Avatar
Member

Join Date: Oct 2016
Posts: 422

11-15-17, 07:44 PM   #16 (permalink)  
No, but if this unit is already busted up and you haven’t even installed it yet, it may be best to keep looking.

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,892
NJ

11-15-17, 07:56 PM   #17 (permalink)  
You won't have any vacuum on the pressure switch if the inducer is missing blades. The vacuum level cannot be felt with your finger. You need to use a manometer.


~ Pete ~

 
TomBurns's Avatar
Member

Join Date: Nov 2017
Posts: 10

11-18-17, 02:22 PM   #18 (permalink)  
American Standard Furnace

PJ you led me in the right direction thanks you for the info. After changing the fan wheel for 30 bucks the furnace runs great.

 
PJmax's Avatar
Group Moderator

Join Date: Oct 2012
Posts: 38,892
NJ

11-18-17, 02:26 PM   #19 (permalink)  
That's great news. Good job.


~ Pete ~

 