manometer accuracy

Reply

  #1  
Old 02-12-18, 08:20 PM
Member
Thread Starter
Join Date: Oct 2008
Location: st pete florida
Posts: 133
manometer accuracy

What is a good reasonable priced accurate manometer to measure my barometric damper?

My furnace should be 0.025 and my flue should be -0.02. Looking at the gauges for sale i see accuracy (read
inaccuracy) ratings that would make readings in the range that I need almost useless. Exp:

0.3% of full scale 55.00wc (0.003x55=0.165) Does that mean that a reading of 0.02 could be off by as much as 0.165?

+/-0.3% of full scale 83.02 InH2O NKTECH NK-L3 (0.003x83.02=0.249)

1.5% of full scale 4.00wc Dwyer 478A-0 (0.15x4=0.6)

Am I doing something wrong here?


tks,
pa
 
Sponsored Links
  #2  
Old 02-13-18, 06:14 AM
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 17,938
I would look for a instrument that is more appropriate for the pressure you're trying to read. A gauge capable of reading up to 55" WC is way too high for your very low pressure application. It's like using a 3'000 psi gauge to check the 30 psi in your car's tires. There are gauges that max out at .5 so any inaccuracy would be very minimal. Dwyer makes some simple plastic gauges that are quite inexpensive and has the scale expanded at the low end for increased accuracy and probably would be perfect for what you're doing.

 
  #3  
Old 02-13-18, 06:37 AM
Member
Thread Starter
Join Date: Oct 2008
Location: st pete florida
Posts: 133
none that Ive found. that dwyer shown +/-3.0 of 3.0 is 0.09, so a reading of 0.02 could be anywhere from 0.11 to -0.07
 
  #4  
Old 02-13-18, 08:25 AM
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 17,938
I would not over think it. A liquid in tube meter is about as accurate as you can get without spending a lot of money. Much of the accuracy will come from how level you install the gauge and set the zero.
 
  #5  
Old 03-07-18, 04:24 PM
Member
Thread Starter
Join Date: Oct 2008
Location: st pete florida
Posts: 133
manometer accuracy take 2

I need to measure -0.02 and +0.03wc.

mount it inclined 10:1 for 10 times the resolution. https://www.amazon.com/Yellow-Jacket-78075-Water-
Manometer/dp/B0038QHTK2/ref=sr_1_5?ie=UTF8&qid=1520466840&sr=8-5&keywords=manometer

its graduated at 0.25 intervals and you can easily judge 1/5 of that. So, 0.25 included 10:1 the 0.25 would then be 0.025 and I could fairly accurately judge 1/5 of that or 0.005.

thoughts?
 
  #6  
Old 03-07-18, 04:29 PM
Member
Thread Starter
Join Date: Oct 2008
Location: st pete florida
Posts: 133
  #7  
Old 03-07-18, 07:28 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 45,548
Take 2 ???
A single topic is contained in a single thread. Threads combined.
 
  #8  
Old 03-07-18, 07:39 PM
Member
Join Date: Oct 2008
Location: New England
Posts: 10,024
Minneapolis has upgraded their manometers to the DG1000 so you might be able to pick up a used DG700, still expensive but certainly can measure pressures with the accuracy you are asking for.
https://www.ebay.com/i/302660358408?chn=ps

Bud
 
  #9  
Old 03-07-18, 08:01 PM
Member
Thread Starter
Join Date: Oct 2008
Location: st pete florida
Posts: 133
Originally Posted by PJmax View Post
Take 2 ???
A single topic is contained in a single thread. Threads combined.
if you dont fully understand and combine threads you do a disservice!
 