Rheem Classis 90 wont heat
#1
Member
Thread Starter
Join Date: Feb 2018
Location: usa
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Rheem Classis 90 wont heat
i am sorry.. I should have paid more attention when my dad was trying to show me what to do//
My classis 90 wont heat.. I hear it trying to go though the cycle.. but no heat comes up through the vent.. the trouble error codes show 2 green light and the left one is blinking slowly.. looks like once .. I dont see a amber light anywhere. Does that mean there is no flame? I hear it trying to light... but never hear the burner start.. Can someone please help.. I dont want to call in a repair man.. I am totally disabled and on a fixed income..
My classis 90 wont heat.. I hear it trying to go though the cycle.. but no heat comes up through the vent.. the trouble error codes show 2 green light and the left one is blinking slowly.. looks like once .. I dont see a amber light anywhere. Does that mean there is no flame? I hear it trying to light... but never hear the burner start.. Can someone please help.. I dont want to call in a repair man.. I am totally disabled and on a fixed income..
#2
Welcome to the forums.
Although I understand your position.... furnaces are not really DIY repair items. My first recommendation is to call your gas provider. They have good techs and fair pricing..... if they offer in-home servicing.
The two flash code is most likely an issue with the pressure switch. It could be the draft inducer not running correctly or not starting at all. Problems with the exhaust flue. Clogged pressure switch hose.
Classic 90 is just a group encompassing many different furnace models. The actual model number, which is needed, is on an ID tag on the side wall inside near the burner.
Although I understand your position.... furnaces are not really DIY repair items. My first recommendation is to call your gas provider. They have good techs and fair pricing..... if they offer in-home servicing.
The two flash code is most likely an issue with the pressure switch. It could be the draft inducer not running correctly or not starting at all. Problems with the exhaust flue. Clogged pressure switch hose.
Classic 90 is just a group encompassing many different furnace models. The actual model number, which is needed, is on an ID tag on the side wall inside near the burner.
#3
Member
The code schematic should be on the back of the access door.
I think this should be close for your furnace-
FLAME LED
The FLAME LED is an indication of the presence of flame.
OFF – No flame is detected.
Rapid Blink – Unexpected Flame
Slow Blink – Marginal Flame Sense
Steady ON – Normal Flame Detected
STATUS LED
The STATUS LED is an indication of a fault present.
Steady ON – Normal Fault detected.
1 Blink – Ignition failure – 1 HR lockout
2 Blinks – Pressure switch stuck open switch will not close when inducer is on.
3 Blinks – Limit switch open main limit or roll-out control.
4 Blinks – Pressure switch stuck closed. Switch will not open.
5 Blinks – Not applicable.
6 Blinks – Line and Neutral reversed.
POWER LED
The POWER LED is an indication of 24ac power to the board.
OFF – No power (24VAC) to control board.
ON – Control is powered
Do you have tools and a meter, and are you ok working around gas and electricity?
I think this should be close for your furnace-
FLAME LED
The FLAME LED is an indication of the presence of flame.
OFF – No flame is detected.
Rapid Blink – Unexpected Flame
Slow Blink – Marginal Flame Sense
Steady ON – Normal Flame Detected
STATUS LED
The STATUS LED is an indication of a fault present.
Steady ON – Normal Fault detected.
1 Blink – Ignition failure – 1 HR lockout
2 Blinks – Pressure switch stuck open switch will not close when inducer is on.
3 Blinks – Limit switch open main limit or roll-out control.
4 Blinks – Pressure switch stuck closed. Switch will not open.
5 Blinks – Not applicable.
6 Blinks – Line and Neutral reversed.
POWER LED
The POWER LED is an indication of 24ac power to the board.
OFF – No power (24VAC) to control board.
ON – Control is powered
Do you have tools and a meter, and are you ok working around gas and electricity?