Amana AMH951155DXAA open high limit without heat turning on


  #1  
Old 03-30-18, 08:02 AM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
Amana AMH951155DXAA open high limit without heat turning on

Hi,
My blower was continuously on for (had been running for hours). I reset the furnace by turning of the power. Upon turning it back on I checked the error code. 4 flashes ..open limit. I checked all for limit 2 high limit and even 2 roll out limit. All have continuity. I jumped all 4 to test. Still same error code. Wiring diagram shows 3 limit switches but I only found 2

the error code and fan blower is on as soon as I turn on the power to the furnace. I also switched th control board because it had a loose connection

any ideas what could be causing it
 
  #2  
Old 03-30-18, 09:30 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
Did you pull the wires off when checking limits ?
 
  #3  
Old 03-30-18, 09:35 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,035
Received 3,415 Upvotes on 3,063 Posts
Welcome to the forums.

I also switched th control board because it had a loose connection
You replaced the board and still have the same problem ?

You need to check the limit circuits right at the control board 12 pin connector.
One circuit is pins #1 and #7. The other circuit is pins # 5 and #11.
There should be 0v across either set of pins on the connector.
 

Last edited by PJmax; 03-30-18 at 03:53 PM.
  #4  
Old 03-30-18, 10:01 AM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
I did pull them and pulled the lines off
 
  #5  
Old 03-30-18, 10:08 AM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you for the welcome

It's with the furnace on and calling for heat correct?
 
  #6  
Old 03-30-18, 10:18 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,035
Received 3,415 Upvotes on 3,063 Posts
If you mean furnace powered..... yes. There won't be any power to measure for if it's off. You are looking for no voltage across the pairs of pins I listed with the plug in place. Doesn't need to be calling for heat.
 
  #7  
Old 03-30-18, 12:53 PM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by PJmax View Post
Welcome to the forums.


You replaced the board and still have the same problem ?

You need to check the limit circuits right at the control board 12 pin connector.
One circuit is pins #1 and #7. The other circuit is pins # 8 and #11.
There should be 0v across either set of pins on the connector.
I checked both sets ...

1 and 7 0v
8 and 11 27v
 
  #8  
Old 03-30-18, 01:32 PM
R
Member
Join Date: Oct 2016
Posts: 2,134
Received 183 Upvotes on 169 Posts
Well, you just found your open circuit.
 
  #9  
Old 03-30-18, 01:48 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,035
Received 3,415 Upvotes on 3,063 Posts
That limit loop shows as two manually resetable limit sensors. More than likely one of the two flame rollout switches over the burner has tripped. They should have a little red button on them for resetting.

Name:  frs.jpg
Views: 1536
Size:  4.3 KB
 
  #10  
Old 03-30-18, 01:56 PM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
I tested both .. they have continuity and I have pressed the reset button to no avail
 
  #11  
Old 03-30-18, 02:11 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,035
Received 3,415 Upvotes on 3,063 Posts
Then you need to trace the wiring that connects pin #8 to #11. Something in that loop is open. It's hard to tell from looking at the service manual as it only shows a generic circuit diagram. The actual diagram is usually posted on the back of the blower door,
 
  #12  
Old 03-30-18, 02:24 PM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by PJmax View Post
Then you need to trace the wiring that connects pin #8 to #11. Something in that loop is open. It's hard to tell from looking at the service manual as it only shows a generic circuit diagram. The actual diagram is usually posted on the back of the blower door,
Pin 8 is ground ...

the wiring diagram is torn ..

the rollout switches are orange and red with a pink wire connecting them

it looks like I should have checked pin 5 ...

across pin 5 and 11 .. 0v
 
  #13  
Old 03-30-18, 02:30 PM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
I checked my thermostat ... it's a nest ..

it's giving error E102 .. problem with W1
 
  #14  
Old 03-30-18, 02:39 PM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
This is my user manual .. by comparing what's left of the diagram on the furnace with my manual it looks identical
 
Attached Images  
  #15  
Old 03-30-18, 04:09 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,035
Received 3,415 Upvotes on 3,063 Posts
My apologies. On my manual it looks like an 8. You are correct..... it is a 5. I've changed my original post.
 
  #16  
Old 03-30-18, 04:17 PM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by PJmax View Post
My apologies. On my manual it looks like an 8. You are correct..... it is a 5. I've changed my original post.
No worries I originally tested pin 6 because I also misread it ..

but across the correct pins I get 0v ... could the thermostat or w1 wire be the cause of the error message and fan running continuously?

in the diagram it shows the limit circuit connecting to the w terminal ... it's in the upper right corner of the diagram
 
  #17  
Old 03-30-18, 04:33 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,035
Received 3,415 Upvotes on 3,063 Posts
Pin 7 coming out of the board should be 24vac when measured to common. After is passes thru the limit switches it should present 24vac to the W1 terminal as long as the stat is not calling for heat.
 
  #18  
Old 03-30-18, 04:58 PM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
I ended up wiring the furnace direct and it works ... so the problem lies with the wires or the thermostat
 
  #19  
Old 03-30-18, 05:01 PM
R
Member
Join Date: Oct 2016
Posts: 2,134
Received 183 Upvotes on 169 Posts
The Nest has a long reputation of causing equipment problems.
Is this wired up for power stealing, or does the Nest have a common?
 
  #20  
Old 03-30-18, 09:16 PM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by roughneck77 View Post
The Nest has a long reputation of causing equipment problems.
Is this wired up for power stealing, or does the Nest have a common?

It was only connected with g w y r1 no common
 
Attached Images  
  #21  
Old 03-30-18, 09:22 PM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
Furnace works fine with old thermostat

I don't understand what happened ... it was working fine for almost a year ... only change was I connected my humidifier aprilaire 700 it worked for a few days without issue ..

it had never worked .. I wired it without the humidistat ... it had some kind of loose connection so I connected valve directly to pressure switch and c on board .. it would only run when calling for heat .. but had 24v even if there was no call for heat .. but like I said it ran fine for a few days
 
  #22  
Old 03-30-18, 09:58 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,035
Received 3,415 Upvotes on 3,063 Posts
Not sure I'm following you on the humidifier. Is that an older Aprilaire 700 ?
Almond or gray case ?

The older almond colored 700's need a relay for a nest connection.
 
  #23  
Old 03-30-18, 10:26 PM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
It's the older unit ... almond case ...

I bypassed the humidistat.... I connected the a the humidifier's solenoid harness directly to the pressure switch using the brown jumper cable and the c spot on the control board

My humidistat works intermittently.. so I decided to by pass it as my house is in the 20s% for humidity

the humidifier worked for a few days then I started having the issues with the Limit switch circuit (thermostat ended up being the issue)
 
Attached Images    
  #24  
Old 03-31-18, 12:14 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,035
Received 3,415 Upvotes on 3,063 Posts
Your older 700 has it's own built in 24vac supply. You cannot connect those two leads directly to a furnace or a nest. Connecting it to your nest probably caused the problem/damage. To confirm this..... short the two leads coming out of the humidifier..... it it starts..... it will need a relay to be connected to the furnace or the nest.
 
  #25  
Old 03-31-18, 03:41 AM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
I will try that ... it does have a transformer but it was connected to it separately... I purchased the homme 4 years ago .. it had never worked I did change the sensor relay ... which is why I tried connected it directly to the c terminal and pressure switch on the furnace bypassing the humidistat 56
 
Attached Images  
  #26  
Old 03-31-18, 05:21 AM
R
Member
Join Date: Oct 2016
Posts: 2,134
Received 183 Upvotes on 169 Posts
It is not permitted to tie into the furnace safety switch loop like that.
Connections for humidifiers and other accessories should be done via the low voltage control connections.
 
  #27  
Old 03-31-18, 07:55 AM
H
Member
Thread Starter
Join Date: Mar 2018
Posts: 15
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by roughneck77 View Post
It is not permitted to tie into the furnace safety switch loop like that.
Connections for humidifiers and other accessories should be done via the low voltage control connections.

I followed these directions
 
Attached Images     
 