Lennox furnace does not ignite
Single stage gas furnace in a 1 story house.
Model number: ML180UHE
Sequence of events.
Any help would be appreciated.
Model number: ML180UHE
- Ac works fine.
- Furnace stopped working suddenly and will not work.
- No error codes from board
- For diagnosing, Stat W wire is connect to Rh to dive constant heat signal
Sequence of events.
- Blower motor turns on
- Pressure sensor senses low pressure
- Ignitor turns on for 20 seconds as specified timeline in the manual
- Gas valve should now turn on for 4 seconds.
- Does not turn on
- No voltage detected
- I heard a click from the board
- Ignitor immediately turns off after the 20 seconds (I would think this would stay on during the 4 seconds)
- This cycle repeats indefinitely
Any help would be appreciated.