Furnace problem.

I am a recently retired HVAC tech yet a bit rusty. I have a Goodman GKS90904CXAE I am working on and am stumped. Someone else already started messing with it so there's that...

Nothing comes on. Of all the tests I have ran all the high voltage is good. 120 at the switch. 120 at the door switch, 120 at the board , 120 at the transformer. No 24 at the board or coming out of the transformer. No LED light. I am thinking transformer or board but want to be sure. Thoughts?
 
Sponsored Links
  #2  
Old 10-30-18, 09:21 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,914
Received 260 Votes on 245 Posts
Welcome to the forums.

120vAC going in to the transformer is good.
You need to check for 24vAC coming out of the transformer. If it's not present.... the transformer is bad. You may want to consider adding in a 3-4A fuse if there isn't one on the control board.
 
  #3  
Old 10-30-18, 09:28 AM
Member
Thread Starter
Join Date: Oct 2018
Posts: 2
Upvotes: 0
Received 0 Votes on 0 Posts
There is not 24 coming out of the transformer. The board has a 3 amp fuse and it's good.
 
  #4  
Old 10-30-18, 09:34 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,914
Received 260 Votes on 245 Posts
Time for a new transformer. Get a 24vAC 40va replacement.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: