The Heat Is On (sometimes...)


  #1  
Old 11-11-18, 07:03 PM
S
Member
Thread Starter
Join Date: Nov 2018
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
The Heat Is On (sometimes...)

Luxaire
G8D10012UHB11a

After the furnace has been idle for several hours, there is a very good chance (~75%) it will not provide heat when the furnace places an order. What happens when it doesn’t work:
- the thermostat places the order
- the fan starts
- the surface ignitor begins to glow, then goes dark
- the fan continues

The remedy that works 100% of the time:
- turn off the switch on the outside of the furnace
- wait 30-60 seconds
- turn on switch
- furnace works fine until the next long idle period

Any ideas what the problem(s) might be?
 
  #2  
Old 11-11-18, 07:25 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
There should be a small clear lens in the blower door. Look inside for a blinking LED.
Count the flashes for the trouble code. The codes are on the back of the blower door.
 
  #3  
Old 11-12-18, 04:52 AM
S
Member
Thread Starter
Join Date: Nov 2018
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
There is indeed a lens, but I have not seen a blinking LED. Will it be there all the time, or just when something isn't working properly?
 
  #4  
Old 11-12-18, 10:42 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
Remove the blower door. Look at the control board. In the bottom corner you will see the LED. The codes are right on that board. I think it should blink continuously with no call for heat. Opening the blower door lets a safety switch open to disconnect power. You can hold that in to observe operation. Once the switch is released.... the codes are erased.
 
  #5  
Old 11-13-18, 05:30 AM
S
Member
Thread Starter
Join Date: Nov 2018
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks, Pete!

I'll eyeball it again and report back ASAP.
 
  #6  
Old 11-13-18, 01:56 PM
S
Member
Thread Starter
Join Date: Nov 2018
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
I removed the blower door, and located the LED and the codes. The LED was not blinking.

I held in the safety switch, and the LED lit for about one second and stopped.

While continuing to hold in the safety switch, I called for heat. The operation failed to produce heat:
- the fan started
- the surface ignitor began to glow, then went dark
- the fan continues

Does this get us closer to a solution?
 
  #7  
Old 11-15-18, 04:48 AM
S
Member
Thread Starter
Join Date: Nov 2018
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
* bump *

Anybody have any ideas?
 
  #8  
Old 11-15-18, 08:27 AM
R
Member
Join Date: Oct 2016
Posts: 2,137
Received 185 Upvotes on 169 Posts
Was a code displayed when you were holding in the switch and the unit failed to ignite?
 
  #9  
Old 11-15-18, 07:47 PM
S
Member
Thread Starter
Join Date: Nov 2018
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Nope. The LED did nothing.
 
 