Furnace whistling when burners start

Reply

  #1  
Old 11-13-18, 07:54 AM
Member
Thread Starter
Join Date: Nov 2018
Posts: 3
Upvotes: 0
Received 0 Votes on 0 Posts
Furnace whistling when burners start

I have 1 year old carrier performance 2 stage furnace. I have notice that when it goes to stage one it starts whistling. I check gas pressure for high and low manifold. both in spec. I check gas coming in and its fine. I also look when its happening and it goes like that.

1. blower off. - no noise
2. inducer motor on, no flame - no noise.
3. inducer motor on hot surface on - no noise.
4. inducer motor on and burners starts on stage1 (lo heat) - whistling noise starts.

it gets less noticeable when blower comes on. but I know every time my furnace starts as i can hear it through the vents and the house. Looks like it goes away in second stage/ high stage of heat.

Any input would be great.
Thank you
 
Sponsored Links
  #2  
Old 11-13-18, 09:12 AM
Member
Join Date: Dec 2004
Location: San Jose,Ca
Posts: 1,560
Upvotes: 0
Received 0 Votes on 0 Posts
That is indicative of an undersized flex connector. I just reread your post and after I saw it goes away on high fire. Maybe I jumped the gun.
 
  #3  
Old 11-13-18, 09:29 AM
Member
Thread Starter
Join Date: Nov 2018
Posts: 3
Upvotes: 0
Received 0 Votes on 0 Posts
mbk3, thanks for replaying. no flex pipe, we have to have hard pipe.
 
  #4  
Old 11-13-18, 11:11 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,477
Received 216 Votes on 205 Posts
Welcome to the forums.

I only service equipment..... no installations and I've noticed a similar issue on units I've worked on. Never on a furnace as new as yours. The noise appears to happen after I've pulled the burner out for cleaning. I always make sure the burner is in just like it came out and tight. There doesn't appear to a rhyme or reason to what causes the noise.

In your case I'd recommend calling back the installing dealer as it may be an issue with the two stage gas valve.
 
  #5  
Old 11-13-18, 09:56 PM
Member
Thread Starter
Join Date: Nov 2018
Posts: 3
Upvotes: 0
Received 0 Votes on 0 Posts
PJmax.

I did call installing dealer and waiting for them to get me on the schedule. Since I have heat and we been getting cold weather I'm not a priority and I don't blame them. They have people without heat out there. I been also talking to a few people and posting online and one suggestion was that my gas valve could be going bad. What do you think about that suggestion
 