LP Furnace flame flutters off and on and doesn't always light

https://youtu.be/h31cvhVHQ1E

https://youtu.be/yy9vCIG04rc
90% effec furnace just replaced rusted out inshots It is usually the middle 2 that flutter, never seen the outside ones do it.
 
Sponsored Links
  #2  
Old 02-09-19, 04:59 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 1,825
Received 93 Votes on 81 Posts
The furnace should have a combustion air control per burner tube. Try adjusting the middle ones to eliminate yellow/orange tips on the flame. They should be blue.
 
  #3  
Old 02-09-19, 06:05 AM
W
Member
Thread Starter
Join Date: Feb 2019
Location: United States
Posts: 5
Received 0 Votes on 0 Posts
There are no adjustments That would be too easy lol
 
  #4  
Old 02-09-19, 06:08 AM
W
Member
Thread Starter
Join Date: Feb 2019
Location: United States
Posts: 5
Received 0 Votes on 0 Posts
I just had the furnace serviced with the old inshots. Without taking a micrometer to measure the new burners with the old, they compared side by side to be equivalent
 
  #5  
Old 02-09-19, 06:19 AM
W
Member
Thread Starter
Join Date: Feb 2019
Location: United States
Posts: 5
Received 0 Votes on 0 Posts
old inshots



New ones in furnace may have to remove burner box again and take pic of them
 
Attached Images   
  #6  
Old 02-09-19, 07:37 AM
R
Member
Join Date: Oct 2016
Posts: 1,945
Received 106 Votes on 100 Posts
What is gas pressure?
The nozzles could be clogged as well.
 
  #7  
Old 02-09-19, 10:20 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,855
Received 1,204 Votes on 1,114 Posts
That's not an air or burner issue.

It's either low propane pressure or more likely clogged orifices. When you take the burner out..... there is a little tiny hole where the propane enters the burner. Propane has more "junk" in the fuel and clog up orifices faster than with natural gas. I'd clean all of them.
 
  #8  
Old 02-09-19, 04:20 PM
W
Member
Thread Starter
Join Date: Feb 2019
Location: United States
Posts: 5
Received 0 Votes on 0 Posts
Thank you for the replies. It has been stupid cold the last week and I'm down to less than 20% in tan

Don't remember which one that one was. I wondered about gas pressure

Name:  orifice.jpg
Views: 309
Size:  30.0 KB
 

Last edited by PJmax; 02-09-19 at 06:04 PM. Reason: added pic from link
  #9  
Old 02-09-19, 06:03 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,855
Received 1,204 Votes on 1,114 Posts
With under 20% liquid you're not getting a whole lot of vaporization on a cold day.
I'm sure your pressure is low. Clean all of them while you're in there.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: