York P3HU blowing cold air
#1
Member
Thread Starter
Join Date: Feb 2019
Location: USA
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
York P3HU blowing cold air
Hello,
My furnace is blowing cold air. It is 20 years old and is located in the attic. The fault code 7 flash, as explained in the trouble shooting manual says that a "flame could not be established. This no-light condition occurred 3 times during the call for heat before locking out. This may be cause by low gas pressure, faulty gas valve, faulty hot surface ignitor or burner problem." Where do I start? Your input is greatly appreciated.
My furnace is blowing cold air. It is 20 years old and is located in the attic. The fault code 7 flash, as explained in the trouble shooting manual says that a "flame could not be established. This no-light condition occurred 3 times during the call for heat before locking out. This may be cause by low gas pressure, faulty gas valve, faulty hot surface ignitor or burner problem." Where do I start? Your input is greatly appreciated.
#2
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes
on
37 Posts
Reset the furnace by turning off the power then turning it back on. Have someone set the thermostat to call for heat while you watch in the area of the burners. If you see a glow, the ignitor is OK.
If the flame lights then goes out right away, the problem is likely the flame sensor. Remove & clean with Scotch Brite pad or CLEAN steel wool, reinstall & try again.
If the flame lights then goes out right away, the problem is likely the flame sensor. Remove & clean with Scotch Brite pad or CLEAN steel wool, reinstall & try again.
#3
Member
Thread Starter
Join Date: Feb 2019
Location: USA
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thank you so much! Yes, I actually shut it off and say the furnace ignite with air going through the burners. It then shut off and tried 3 times and then stopped. Going to do what you suggested!
#6
Unfortunately.... If it lights it won't be the igniter. If it runs that long it will not be the flame sensor.
It could be a dirty burner or gas orifice as the flame sensor rod must be kept completely engulfed in the flame.
There are several variations of that series furnace. Post the full model number. It's found inside on the side wall near the burner.
It could be a dirty burner or gas orifice as the flame sensor rod must be kept completely engulfed in the flame.
There are several variations of that series furnace. Post the full model number. It's found inside on the side wall near the burner.