I was wondering if the opening area cut into the side of my furnace is sized properly. There is a 13" x 22" opening where the Aprilaire electronic air cleaner connects to the right side of the furnace. That works out to 286 sq. in.
The furnace is a two stage Amana 62K/92K btu furnace with a 3 ton Amana 2 stage A/C..Does this provide enough air for the heating and cooling?
 
Sponsored Links
  #2  
Old 08-01-19, 08:37 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,589
Received 337 Votes on 315 Posts
Welcome to the forums.

Is the hole in the side of the furnace the same size as the ductwork.
If it's smaller..... that could be a problem.
 
  #3  
Old 08-02-19, 07:58 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,978
Received 21 Votes on 16 Posts
Yea, what PJMax said. What is the size of the return air duct before the electronic air cleaner. My Trion Electronic Air Cleaner is 16" X 25" and rated at 1400 CFM. I doubt your furnace would be moving that many CFM.
 
  #4  
Old 08-02-19, 09:19 AM
Member
Join Date: Oct 2013
Location: United States
Posts: 2,698
Received 11 Votes on 11 Posts
v,
Every ton of cooling equals 400 cfm's so your 3 ton unit is equal to 1200 cfm's. As PJ stated your return trunk should at least equal your supply trunk. A simple rule to remember is you will only get as much air out as you have coming in. You can go bigger with the return but should never go smaller.

Hope this helps a little.
 
  #5  
Old 08-05-19, 12:31 PM
Member
Thread Starter
Join Date: Jul 2019
Posts: 4
Received 0 Votes on 0 Posts
The opening on the side of the furnace is 13" X 22".
The return duct dimensions are 8" X 24" X 40'.
 
  #6  
Old 08-05-19, 01:13 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,589
Received 337 Votes on 315 Posts
So the hole in the furnace is slightly smaller than the duct size.
 
  #7  
Old 08-05-19, 01:50 PM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 1,913
Received 24 Votes on 19 Posts
The hole in the furnace is always a little smaller than the filter.

For a 16x25 filter, the hole may be like 15 x 24 or something.

A smaller than recommended hole can stress the blower motor if it's variable speed or lead to reduced airflow if furnace has a regular multi-speed blower.

To use the entire filter, the hole has to match the outlet of the filter, if it doesn't there needs to be a transition to the smaller size hole.

1400 CFM. I doubt your furnace would be moving that many CFM.
A 90k 95% 'er will move that kind of cfm.

The 80% version, closer to 1200.
 
  #8  
Old 08-05-19, 02:37 PM
Member
Thread Starter
Join Date: Jul 2019
Posts: 4
Received 0 Votes on 0 Posts
Aprilaire 5000

The outlet side ( facing the furnace) of the Aprilaire 5000 air cleaner is 14"-3/4" X 24"-7/8".
If that helps.
 
  #9  
Old 08-06-19, 07:36 PM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 1,913
Received 24 Votes on 19 Posts
the manufacturer should have the hole size in the install manual.

if it can be enlarged a bit, it's a good idea.

there's always a maximum size.
 
  #10  
Old 08-07-19, 04:56 AM
airman.1994's Avatar
Member
Join Date: Dec 2005
Location: VA
Posts: 5,767
Received 4 Votes on 4 Posts
13x22 is good for 1800 cfm at .08 friction loss
 
  #11  
Old 08-08-19, 09:30 AM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 1,913
Received 24 Votes on 19 Posts
when you have a filter, that doesn't apply.

a smaller than normal return opening reduces the effective filter area, increasing pressure drop across it.

unless there's a gap between furnace and filter and a transition to the return air opening.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: