Oil fired furnace exhaust routing: Need help

So i got a older carrier 100,000btu oil furnace and i want to run it in my little shop can i run the exhaust piping up a little and out the side wall?

Name:  ob.jpg
Views: 200
Size:  102.9 KB
 

Last edited by PJmax; 10-02-19 at 04:08 PM. Reason: resized picture
  #2  
Old 10-02-19, 04:09 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,440
Received 4,051 Upvotes on 3,634 Posts
Welcome to the forums.

I'm a service person.... not installer but the flue needs to be concentric (double insulated) if it's passing thru something flammable. It also needs to go up high enough on the building to create a draft.
 
  #3  
Old 10-02-19, 04:35 PM
G
Member
Thread Starter
Join Date: Oct 2019
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks. I do have double insulated pipe to run through the wall and i have some pipe to go up with but how high and can i use a regular 4 way vent cap?

Name:  cap.jpg
Views: 151
Size:  9.7 KB
 

Last edited by PJmax; 10-02-19 at 09:26 PM. Reason: resized picture
 