New blower wont stop nothing else working

Hello I have a gas furnace Heil model nule100bg01. About a month ago we had a power outage and the ac stopped working looked to be the blower motor and capacitor, wouldn't move when put directly to 120v so I replaced it. The new blower wont turn off except when I kill the power and the control board does not seem to be getting power I have a backup control board I tried but didn't do anything. What should I be checking the transformer, limit switch or something I haven't thought of
 
Sponsored Links
  #2  
Old 10-09-19, 11:38 AM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 1,941
Received 28 Votes on 23 Posts
some boards have a optional continuous fan connection energized all the time when there's no call for heating or cooling - check yours.

would need to see a schematic to advise further.
 
  #3  
Old 10-09-19, 11:55 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,706
Received 344 Votes on 322 Posts
Welcome to the forums.

The wiring diagram off the blower door is always a major plus for us..... How-to-insert-pictures.

In your case..... with no red LED from the board..... you need to check the 24vAC transformer.
Don't forget the blower door safety switch. When the door is off.... everything is dead.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: