Furnace Burners Ignite Then Shut Off

I have a Weather King furnace, and it is not working properly. When I turn it on, I hear the system starting. It takes approximately 15-20 seconds for the burners to ignite. They stay on for about 5-6 seconds and then shut off. The system will repeat this again 2 more times, and the same thing happens. Is there anything that I can do to troubleshoot this? I can post pictures if that would help. I donít have much HVAC experience, but I have done a lot of electrical. Iím not sure if that helps at all.
 
Sponsored Links
  #2  
Old 10-19-19, 12:58 PM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 1,990
Received 35 Votes on 30 Posts
check for an error code.

likely just a dirty flame sensor.
 
  #3  
Old 10-19-19, 02:55 PM
Member
Thread Starter
Join Date: Jun 2015
Posts: 241
Received 0 Votes on 0 Posts
Is this error code displayed by the green led on the control board? It blinks 2 times, then goes out, blinks 2 times, etc.
 
  #4  
Old 10-19-19, 03:25 PM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 1,990
Received 35 Votes on 30 Posts
the error codes should be listed on the schematic - open the blower compartment access panel and check the side that normally faces in.
 
  #5  
Old 10-19-19, 04:47 PM
Member
Thread Starter
Join Date: Jun 2015
Posts: 241
Received 0 Votes on 0 Posts
I checked the schematic, and it says 2 blinks is ďPressure Switch Open.Ē I donít know if this matters, but my blower went in July. It was replaced with a new one. The AC worked fine after that. I donít know if that would have anything to do with this.
 
  #6  
Old 10-19-19, 05:35 PM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 1,990
Received 35 Votes on 30 Posts
No it doesn't.

Monitor voltage drop across the pressure switch during the cycle, see if/when it drops off.

Set your meter to read ac volts - you're looking for 24v ac +/-.

If the switch is dropping out, disconnect the pressure switch hoses and make sure the hose and connections are clear.

If you have a high efficiency furnace vented with plastic pipe, make sure the drain lines and trap are clear.

Check the intake and exhaust outside for blockages.
 
  #7  
Old 10-24-19, 02:11 PM
Member
Thread Starter
Join Date: Jun 2015
Posts: 241
Received 0 Votes on 0 Posts
I hadnít responded, but I was able to get the unit working on Sunday. I didnít do anything complicated. I checked the hoses, disconnected the wires on the pressure switches, and cleaned the terminals. There didnít seem to be any debris anywhere. I also cleaned the flame sensor. It started working and was fine until this morning. Itís doing the same thing again. I got my multimeter and tested both pressure switches. When the unit calls for heat, the voltage goes to 26v and then 0. The burners are on for about 3-5 seconds and then turn off. When the unit turns off, I donít see much of a jump on my multimeter, but it does occasionally say OL. Any advice would be greatly appreciated.
 
  #8  
Old 10-24-19, 02:31 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,245
Received 381 Votes on 358 Posts
When the unit calls for heat, the voltage goes to 26v and then 0.
That is the normal response of the pressure switch.
It should stay at 0v as long as the inducer blower is running.

You are checking for voltage. The meter should be on an AC scale over 24vAC.
OL typically only appears when you are in ohms mode.

Are you still getting a code for open pressure switch ?
Pull the pressure switch hose off of the inducer and clean the tiny orifice down inside the fitting.
You can use a pin, a broom bristle or small drill bit.

Pressure switch issues can be tough to localize. You may need to call in a service tech on this one.

Name:  DI nipple.jpg
Views: 24
Size:  8.2 KB
 
  #9  
Old 10-24-19, 03:27 PM
Member
Thread Starter
Join Date: Jun 2015
Posts: 241
Received 0 Votes on 0 Posts
Thanks, PJ. I may have to call a tech in on this one. It's over my skill level. What's so odd is that I actually got it working for 4 days. I thought maybe there was an exhaust blockage, but I doubt I would have gotten it to work at all. I'm still getting the pressure switch error, but I'm wondering if it's possible that's it's a bad flame sensor. I disconnected it just to see what would happen, and it seems to be doing the exact same thing.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: