Furnace Burners Ignite Then Shut Off
#1
Member
Thread Starter
Furnace Burners Ignite Then Shut Off
I have a Weather King furnace, and it is not working properly. When I turn it on, I hear the system starting. It takes approximately 15-20 seconds for the burners to ignite. They stay on for about 5-6 seconds and then shut off. The system will repeat this again 2 more times, and the same thing happens. Is there anything that I can do to troubleshoot this? I can post pictures if that would help. I don’t have much HVAC experience, but I have done a lot of electrical. I’m not sure if that helps at all.
#3
Member
Thread Starter
Is this error code displayed by the green led on the control board? It blinks 2 times, then goes out, blinks 2 times, etc.
#4
the error codes should be listed on the schematic - open the blower compartment access panel and check the side that normally faces in.
#5
Member
Thread Starter
I checked the schematic, and it says 2 blinks is “Pressure Switch Open.” I don’t know if this matters, but my blower went in July. It was replaced with a new one. The AC worked fine after that. I don’t know if that would have anything to do with this.
#6
No it doesn't.
Monitor voltage drop across the pressure switch during the cycle, see if/when it drops off.
Set your meter to read ac volts - you're looking for 24v ac +/-.
If the switch is dropping out, disconnect the pressure switch hoses and make sure the hose and connections are clear.
If you have a high efficiency furnace vented with plastic pipe, make sure the drain lines and trap are clear.
Check the intake and exhaust outside for blockages.
Monitor voltage drop across the pressure switch during the cycle, see if/when it drops off.
Set your meter to read ac volts - you're looking for 24v ac +/-.
If the switch is dropping out, disconnect the pressure switch hoses and make sure the hose and connections are clear.
If you have a high efficiency furnace vented with plastic pipe, make sure the drain lines and trap are clear.
Check the intake and exhaust outside for blockages.
#7
Member
Thread Starter
I hadn’t responded, but I was able to get the unit working on Sunday. I didn’t do anything complicated. I checked the hoses, disconnected the wires on the pressure switches, and cleaned the terminals. There didn’t seem to be any debris anywhere. I also cleaned the flame sensor. It started working and was fine until this morning. It’s doing the same thing again. I got my multimeter and tested both pressure switches. When the unit calls for heat, the voltage goes to 26v and then 0. The burners are on for about 3-5 seconds and then turn off. When the unit turns off, I don’t see much of a jump on my multimeter, but it does occasionally say OL. Any advice would be greatly appreciated.
#8
When the unit calls for heat, the voltage goes to 26v and then 0.
It should stay at 0v as long as the inducer blower is running.
You are checking for voltage. The meter should be on an AC scale over 24vAC.
OL typically only appears when you are in ohms mode.
Are you still getting a code for open pressure switch ?
Pull the pressure switch hose off of the inducer and clean the tiny orifice down inside the fitting.
You can use a pin, a broom bristle or small drill bit.
Pressure switch issues can be tough to localize. You may need to call in a service tech on this one.

#9
Member
Thread Starter
Thanks, PJ. I may have to call a tech in on this one. It's over my skill level. What's so odd is that I actually got it working for 4 days. I thought maybe there was an exhaust blockage, but I doubt I would have gotten it to work at all. I'm still getting the pressure switch error, but I'm wondering if it's possible that's it's a bad flame sensor. I disconnected it just to see what would happen, and it seems to be doing the exact same thing.