Blower Motor or Controller


  #1  
Old 11-01-19, 11:55 AM
D
Member
Thread Starter
Join Date: Nov 2019
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Blower Motor or Controller

I have a Consolidated Industries Model HDA100HN5R AC/Furnace. My problem is with the blower motor. I don't use the AC function, just the furnace.
When I started the system this season, the blower motor worked normally. The second cycle the motor ran at half speed. The next few cycles the motor continued to run a half speed. Now the motor won't run at all.
I'm not sure if the problem is with the motor or the controller. I would appreciate any thoughts on how to determine where the problem lies.
Thanks.
 
  #2  
Old 11-01-19, 01:23 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
Welcome to the forums.

Sorry.... I can find any unit by that model number.
See if you can find a wiring diagram on the wiring access cover. We'll probably need to see that.

You're going to need a meter to check for supply voltage to the motor. That will determine if it's a board problem or a motor problem.
 
  #3  
Old 11-01-19, 03:05 PM
D
Member
Thread Starter
Join Date: Nov 2019
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Blower Motor or Controller

Here is the wiring diagram.
 
Attached Images  
  #4  
Old 11-01-19, 03:08 PM
D
Member
Thread Starter
Join Date: Nov 2019
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Once I got the cover off, I did notice that the Diagnostic Light was flashing 4 times. I'm assuming there is no circulation airflow.
 
  #5  
Old 11-02-19, 12:47 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Hi, do you have a multi meter? Locate the Speed select relay, trace the wiring back from the motor, with one lead of the meter to ground and the furnace calling for heat place the other lead of the meter to each of the terminals on the relay and determine which one has 120 volts, it should be either Red or Blue.

Geo
 
  #6  
Old 11-07-19, 07:20 PM
D
Member
Thread Starter
Join Date: Nov 2019
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the reply. I did check the blue lead and it fluctuated between 118.5 and 119.1 volts. When I was checking and the fan received power, it hummed and didn't start turning until I gave it a "nudge". Then it started to run at the correct speed, with no noise or other issues. Could it be the capacitor?
 
  #7  
Old 11-07-19, 07:50 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
Since you've measured the proper voltage...... the board is ok.
Yes.... it could be a capacitor or worn out bearings.
 
  #8  
Old 11-07-19, 10:37 PM
D
Member
Thread Starter
Join Date: Nov 2019
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Blower Motor or Controller

Attachment 110790Thank you, Pjmax. I'm going to start with the less expensive option and change the capacitor first.
As my luck would have it, the uf and model numbers are illegible on the capacitor that I removed, see photo. It looks like it could be 10uf. I've read that the wrong uf number can mess up my motor.
 
Attached Images  
  #9  
Old 11-08-19, 04:39 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Hi, looks like 10 UF, is there anything on the motor nameplate as to Cap size?
Geo
 
  #10  
Old 11-08-19, 03:43 PM
D
Member
Thread Starter
Join Date: Nov 2019
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Geochurchi, there was a plate on the motor. As my luck would have it, it was under the strap holding the motor. I was able to move the strap enough to see that it was 10uF. One quick to Grainger and $5.96 later, I now have a working heater again. Especially since the weatherman is saying we might be breaking record lows here in Birmingham Alabama.
Many thanks to you and Pjmax for your help.
 
  #11  
Old 11-08-19, 09:11 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
Good job. Name:  thumb.jpg
Views: 58
Size:  1.6 KB Thanks for letting us know how you made out.
 
 