Trane furnace runs for hours or days then stops.

I have a Trane xv80 furnace. It will run for anywhere from 12 hours to 3 days without fault, then stop with the induction fan running constant. It is giving me a pressure switch code. A friend that works in HVAC said the switch going is a common problem. I replaced it last Tuesday, it ten great until Friday afternoon. Then stopped again. I have checked for blockage in the line, the filter is clean, as stated earlier the fan runs just fine. If I flip off the power supply for a few seconds, it will restart and run again. Iím terrified of heights, and our roof has a steep pitch, so I have not gone up to check the vent. Is there anything else I may be missing beside checking the vent?
 
Sponsored Links
  #2  
Old 11-11-19, 04:20 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 55,201
Received 595 Votes on 560 Posts
Welcome to the forums.

Pressure switches rarely go bad. Your problem may be as simple as a little clog. Take the hose off the draft inducer. Get a small drill bit, broom bristle or straight pin and clean out the micro hole in the hose connection. The hole is at the bottom of the fitting. Your cleaning device needs to go in at least an inch.

Name:  DI nipple.jpg
Views: 55
Size:  8.2 KB
 
  #3  
Old 11-11-19, 07:19 PM
T
Member
Thread Starter
Join Date: Nov 2019
Posts: 5
Received 0 Votes on 0 Posts
thank you for your response. I checked for blockage there this morning, and just checked with something longer, it doesnít look or feel like there is anything blocking the inlet.
 
  #4  
Old 11-12-19, 02:12 PM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 2,022
Received 39 Votes on 33 Posts
needs to be checked with a manometer.

could be a failing inducer, bad heat exchanger, blockage right at the exhaust outlet. odd that it's intermittent.
 
  #5  
Old 11-12-19, 02:26 PM
T
Member
Thread Starter
Join Date: Nov 2019
Posts: 5
Received 0 Votes on 0 Posts
Thatís what is so bizarre, itís unpredictable when it will fail or not.
 
  #6  
Old 11-12-19, 04:35 PM
T
Member
Thread Starter
Join Date: Nov 2019
Posts: 5
Received 0 Votes on 0 Posts
Thatís what is so bizarre, itís unpredictable when it will fail or not.
 
  #7  
Old 11-18-19, 10:50 AM
T
Member
Thread Starter
Join Date: Nov 2019
Posts: 5
Received 0 Votes on 0 Posts
Update

Okay, the temperature hasnít dipped below freezing since I posted this, and the heater has had no issues. That leads me to believe that something is icing up, and creating the blockage? Would that make any sense? If so, any ideas on what I need to check?
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: