Furnace not coming on past the inducer fan

Need help with furnace . it comes on with inducer fan but no flame rod or anything then kicks off. Help
 
Sponsored Links
  #2  
Old 11-18-19, 08:35 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,219
Received 477 Votes on 447 Posts
Welcome to the forums.

You aren't giving us much to work with.

On a call for heat...... the inducer starts...... then the pressure switch needs to prove by closing.... then the igniter starts to heat. Your problem sounds like an issue with the flue or pressure switch path.

Many furnaces have a control board with a fault LED in the blower compartment. See if your furnace has a sight glass in the door. Look thru and count the flashes. The codes are on the back of the blower door.
 
  #3  
Old 11-19-19, 07:30 AM
Member
Join Date: Oct 2016
Posts: 1,562
Received 53 Votes on 49 Posts
Furnace make and model?
Error code?
Is the pressure switch closing when the inducer runs?
 
  #4  
Old 11-19-19, 06:51 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,219
Received 477 Votes on 447 Posts
Seems to be an echo in here.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: