Trane XL80 No ignition 3.9 v to igniter during start cycle
#1
Member
Thread Starter
Join Date: Jan 2020
Posts: 3
Received 0 Votes
on
0 Posts
Trane XL80 No ignition 3.9 v to igniter during start cycle
2- 1987 XL80 Furnaces (TUD090A936A0) side by side parallel hookup, 1 furnace is fine the second stopped running sometime in last 5 days. The non running unit at call for heat the white Roger's control (model 50e47-843) comes on, vent fan starts, igniter doesn't glow, only 3.9 volts at igniter wiring from control box.Resistance thru igniter is 1.44 to no cracks. Gas never comes on, I figure it's because no heat from igniter. Need help where to go from here on troubleshooting before throwing money at it (control module). Any help would be appreciated
#2
Here's a link to the manual for the control which includes "blink codes" & troubleshooting. https://climate.emerson.com/document...es-4474772.pdf
#3
Member
Thread Starter
Join Date: Jan 2020
Posts: 3
Received 0 Votes
on
0 Posts
Green Led goes to slow blink red after exceeding ignition recycling. I can reset and the same sequence starts over. If it wasn't so cold I would swap control out of working furnace. But the sun is down and 15* heading toward 9* overnight
maybe I'll try that tomorrow 28 high
maybe I'll try that tomorrow 28 high
#4
igniter doesn't glow, only 3.9 volts at igniter wiring from control box.
If still low..... the module is bad. It needs to put out 120v to the igniter when heating.
#6
A very common problem is one of the control relays like for the inducer or igniter
gets pitted/arced requiring the board to be replaced.
gets pitted/arced requiring the board to be replaced.