Goodman Gas Furnace GMP075 3 Blinking lights no suction from the inducer motor

Goodman Gas Furnace GMP075 3 Blinking lights no suction from the inducer motor


  #1  
Old 02-17-20, 08:57 AM
S
Member
Thread Starter
Join Date: Sep 2014
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Goodman Gas Furnace GMP075 3 Blinking lights no suction from the inducer motor

So, the fan works, but no flame, 3 blinking lights for "vent or pressure switch vent blockage"
I've seen a couple of related messages for the similar situation and I followed instructions and it looks like inducer motor nipple is blocked. If I suck air from the pressure switch, the flame turns on. If I try to suck or blow air into the nipple, it is completely blocked.
I've seen recommendations to use a small drill bit and somewhere is says paper clip, but could not find complete instructions. I can insert paper clip approximately 1 and 1/16 and then gets stuck, while the visible nipple length is approximately 3/4 of an inch. Is it deep enough? I can drill with 1/16 drill bit approx 3/4 of an inch. Not sure what is the right drill diameter and how long each of bit and clip can go to avoid damage.
Also, since this is completely blocked nipple, does it sound safe, until the issues is addressed, to manually shorten the switch connectors at the right time just to warm the house time to time?
 

Top Answer

 
02-17-20, 08:00 PM
fastback
fastback is offline
Member
Join Date: Jun 2014
Location: usa
Posts: 95
Received 21 Upvotes on 18 Posts
https://www.homedepot.com/p/Lincoln-...H575/100341101

In the summer I use these for their designed purpose on AC installs. In the winter I use them to clean out plugged inducer ports.
 
  #2  
Old 02-17-20, 09:50 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,816
Received 3,922 Upvotes on 3,518 Posts
I've never had a port completely blocked off where nothing would go thru. You should be able to push something small enough into the port to hit the fan blades. I use a sharp pointed probe to clean the hole. 1/16" may be too big.

Unfortunately shorting the leads on the pressure switch won't work. The furnace checks for those leads to be open on a call for heat and then go shorted when the inducer starts. If they are shorted from the start you'll get a shorted or closed switch fault code.
 
  #3  
Old 02-17-20, 10:07 AM
S
Member
Thread Starter
Join Date: Sep 2014
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you, will try something smaller and will try deeper.

I can start it "at the right time", after the fan starts, it gives me heating at least time to time when I can shorten it. But hopefully will be able to address the issue soon.
 
  #4  
Old 02-17-20, 12:03 PM
S
Member
Thread Starter
Join Date: Sep 2014
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
A piece of 30G wire did the job. Thank you!
 
  #5  
Old 02-17-20, 12:34 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,816
Received 3,922 Upvotes on 3,518 Posts
So is everything working ok now ?
 
  #6  
Old 02-17-20, 05:10 PM
S
Member
Thread Starter
Join Date: Sep 2014
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes, and even the paper clip I've used before, was little bit too thick, but the wire just went through. Thank you!
 
  #7  
Old 02-17-20, 05:58 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,682
Received 41 Upvotes on 39 Posts
Thirty gauge wire is SMALL. Now that you have an opening, I'd try a small drill bit. With a hole as small as you have I'm really surprized the switch would close.
 
  #8  
Old 02-17-20, 08:00 PM
F
Member
Join Date: Jun 2014
Location: usa
Posts: 95
Received 21 Upvotes on 18 Posts
https://www.homedepot.com/p/Lincoln-...H575/100341101

In the summer I use these for their designed purpose on AC installs. In the winter I use them to clean out plugged inducer ports.
 
Grady, PJmax voted this post useful.
 