Sometimes Blows Cold Air Mind of its Own


  #1  
Old 03-05-20, 05:11 AM
A
Member
Thread Starter
Join Date: Mar 2020
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sometimes Blows Cold Air Mind of its Own

I bought my house a year ago. We noticed this problem as soon as the cold weather hit.

Winchester Gas Furnace. Sometimes it will kick on, take 2 to 3 times to blow air. Sometimes its warm, sometimes its cold and i have to flip the switch and turn it off and back on then its fine. Themostat ticks and sends for heat. I've replaced flame sensor and ignitor. Error code is 7. Had a hvac guy out last year. He cleaned the unit and replaces a part (not sure what part, I've sent them messages to ask but can't get a reply). He also told me to run it without a filter. But doesn't seem to effect the probibility it will blow cold or hot. Any ideas left that I can do without calling out HVAC guy?
 
  #2  
Old 03-05-20, 09:45 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Hi, what is error code 7? there should be documentation somewhere on the furnace, also what is the mdl# of the furnace?
Geo
 
  #3  
Old 03-05-20, 01:44 PM
R
Member
Join Date: Oct 2016
Posts: 2,137
Received 185 Upvotes on 169 Posts
We would need the model number of the furnace, and the diagnostic description for that code.
 
  #4  
Old 03-05-20, 04:31 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,098
Received 3,423 Upvotes on 3,069 Posts
Welcome to the forums.

The parent company for your furnace is York. The link below lists the York fault codes but may not be the correct manual for your furnace.

7 RED FLASHES: This fault code indicates that the flame could not be established. This no-light condition occurred 3 times (2 retries) during the call for heat before locking out. Low gas pressure, faulty gas valve, faulty hot surface igniter or burner problem may cause this. The furnace will lock out for one hour and then restart.

Fault codes at end of manual.
 
  #5  
Old 03-06-20, 05:37 AM
A
Member
Thread Starter
Join Date: Mar 2020
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
My number is G8T 08012DNA11A


7 RED FLASHES: This fault code indicates that the flame could not be established. This no-light condition occurred 3 times (2 retries) during the call for heat before locking out. Low gas pressure, faulty gas valve, faulty hot surface igniter or burner problem may cause this. The furnace will lock out for one hour and then restart.
 

Last edited by Author. Unnonow; 03-06-20 at 05:39 AM. Reason: Added fault code
  #6  
Old 03-06-20, 05:56 AM
R
Member
Join Date: Oct 2016
Posts: 2,137
Received 185 Upvotes on 169 Posts
Low gas pressure, faulty gas valve, faulty hot surface igniter or burner problem may cause this.


The items above, listed under the diagnostic code are where to start your troubleshooting.
 
  #7  
Old 03-06-20, 11:33 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,787
Received 173 Upvotes on 156 Posts
Any ideas left that I can do without calling out HVAC guy?
Yeah, get a new HVAC guy.
 
 

Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: