Wayne oil burner controller Honeywell r8184g switched to r7284u controller
Hi everyone I’m stumped I switched my old Honeywell r8184g to the new r7284u controller when I installed the controller I ran the burner motor and ignition together to the motor spade on the back and then the limit control to the limit spade and the l1 spade and the cad wires to the cad spade connectors and the thermostat to the tt on the front of the r7284u controller it will fire but it will shut off after the burner timer runs out after 30 seconds. I’m at a lose and I feel I’m missing something.
#2
Member
The only wires that go to the CC spades are the yellow cad cell wires from the cad cell itself.
Below is a sight with the install instructions and schematic.