Wayne oil burner controller Honeywell r8184g switched to r7284u controller


  #1  
Old 03-09-20, 07:16 AM
J
Member
Thread Starter
Join Date: Mar 2020
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Wayne oil burner controller Honeywell r8184g switched to r7284u controller

Hi everyone I’m stumped I switched my old Honeywell r8184g to the new r7284u controller when I installed the controller I ran the burner motor and ignition together to the motor spade on the back and then the limit control to the limit spade and the l1 spade and the cad wires to the cad spade connectors and the thermostat to the tt on the front of the r7284u controller it will fire but it will shut off after the burner timer runs out after 30 seconds. I’m at a lose and I feel I’m missing something.
 
  #2  
Old 03-09-20, 02:47 PM
S
Member
Join Date: Oct 2013
Location: United States
Posts: 2,715
Received 132 Upvotes on 124 Posts
The only wires that go to the CC spades are the yellow cad cell wires from the cad cell itself.

Below is a sight with the install instructions and schematic.


https://www.supplyhouse.com/Honeywell-R7284U1004-Universal-Digital-Electronic-Oil-Primary?gclid=Cj0KCQjw0pfzBRCOARIsANi0g0svngsI5CBaRZ41zpQ6A64wrFizbq2_31Q2EjqgaMydLC6XGddfbfQaAoVZEALw_wcB
 
 