Goodman furnace leaking water


  #1  
Old 03-20-20, 02:09 PM
R
Member
Thread Starter
Join Date: Mar 2020
Posts: 1
Received 0 Votes on 0 Posts
Goodman furnace leaking water

The goodman furnace in leaking, after opening the furnace I did find out exactly where its leaking from.
Please suggest how can I resolve this issue.

As you can see in the attached images - the leak is coming from small opening next to the Hose A in Image named "Leak-location" I have marked it with red arrow.
 
Attached Images     
  #2  
Old 03-20-20, 04:49 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 62,543
Received 1,598 Votes on 1,473 Posts
Welcome to the forums.

Thread moved.
Although you may have this furnace in a garage or workshop..... it's considered a standard furnace.

More than likely that is a tell tale fitting since it's above the drain line.
When water comes out of there it means the large drain hose or port is clogged.
Have you tried removing the large line to see if it's full of water ?
 
 