Lennox furnace wont ignite

Model number - ML180UH070P36A-07

air filter brand new, fresh batteries in thermostat, gas is open from main.

thermostat calls for heat
induction motor comes on
hsi gets red hot
”click” happens
no ignition, retries 4 more times and goes into watchguard mode (alternating slow flashes) - burners failed to ignite
this primarily happens at night i dont know if that helps.

i have cleaned flame sensor, cleaned hsi (without touching it) all wires connected, no burnouts on control board.

any help would be appreciated thank you in advance
 
Sponsored Links
  #2  
Old 04-25-20, 07:43 PM
R
Member
Join Date: Oct 2016
Posts: 1,752
Received 93 Votes on 87 Posts
Check the voltage to the gas valve. If you have coil voltage check gas pressure.
 
  #3  
Old 04-25-20, 09:14 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 57,089
Received 840 Votes on 787 Posts
Welcome to the forums.

The HSI is extremely fragile and should never be touched.
I know.... there are many videos telling you to sand the igniter. Wrong.
Usually if there is an igniter problem..... the gas will sometimes light or will light with a boom.
If that igniter doesn't look brilliant white when heating.... replace it.

Roughneck mentioned the gas valve. That's what you need to check next. There should be 24vAC on the two wires for approx 7 seconds before the igniter goes out. If the gas valve has an off/on switch on it...... operate that a few times. Remove the wires from the valve and put them back on. Disconnect the large 12 pin plug on the main board several times. It's very possible to have a corroded contact.
 
  #4  
Old 04-26-20, 07:35 AM
J
Member
Thread Starter
Join Date: Apr 2020
Posts: 3
Received 0 Votes on 0 Posts
I have checked voltage and it has voltage at gas valve i cant remember off hand what it was and will check again. The hsi is definitely glowing red not white when you hear that click. I can replace it it’s relatively inexpensive just hoping its not gas valve issue
 
  #5  
Old 04-26-20, 03:16 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 57,089
Received 840 Votes on 787 Posts
The 24vAC at the gas valve will only be there when the valve should be open.
In other words.... if you are measuring 24v on the valve at all times.... you aren't measuring correctly.
 
  #6  
Old 04-26-20, 07:00 PM
J
Member
Thread Starter
Join Date: Apr 2020
Posts: 3
Received 0 Votes on 0 Posts
Understood, ive been watching a million youtube videos on it i get what youre laying diwn
 
  #7  
Old 04-28-20, 05:48 PM
user 10's Avatar
Member
Join Date: Mar 2004
Location: NA
Posts: 2,043
Received 39 Votes on 33 Posts
Straight from the service manual - do the testing shown in the picture below to make sure the igniter is still good and board is applying appropriate voltage to it.

The ignitor resistance may be too high, preventing it from warming up completely.

It should be bright orange to white when fully warmed up - not red.

 
Attached Images  
  #8  
Old 04-29-20, 04:39 AM
D
Member
Join Date: Feb 2015
Location: US
Posts: 13
Received 4 Votes on 4 Posts
Replace the Gas valve

I replace at least a couple every heating season. Often enough that that GV is truck stock.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: