Ventless heater is not working


  #1  
Old 10-03-20, 12:08 PM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ventless heater is not working

Hi all, I just replaced a ventless heater that was busted with a new ventless heater that was purchased at the same place. The previous one lasted about 15 years. This one looked exactly the same like it was the same listed btu. One difference was that you can run on propane or natural gas. There is a knob to turn for you to select which gas you are using. There is also inlets on the bottom for propane or natural gas. Problem is is that after I installed this new ventless heater everything looked good but for some reason the pilot light would not start. I honestly don't even think gas is flowing because I placed a flame near where the gas should be coming out and nothing happened.

I troubleshot this by thinking it was busted so I was going to return and install a new one but that didn't solve the problem either. What am I missing? I did check the gas at the inlet of the ventless heater and that is flowing. The only thing that I wasn't able to check is the manifold pressure. It does state that I should check that in the manual but I didn't think it would be a problem because I am replacing a ventless heater so there should be proper pressure getting to this new ventless heater.

This is the installation manual for the thing:
http://pdf.lowes.com/installationgui...08_install.pdf

Thanks for helping...
 
  #2  
Old 10-03-20, 12:50 PM
R
Member
Join Date: Oct 2016
Posts: 2,183
Received 199 Upvotes on 181 Posts
You’ll have to check gas pressure.
 
  #3  
Old 10-03-20, 01:01 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
I did check the gas at the inlet of the ventless heater and that is flowing.
How did you do that ??

Natural gas or propane ?
It may take a while for the air to purge out of the gas line.
 
  #4  
Old 10-03-20, 01:24 PM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
I removed the ventless heater from the pipe and then opened the valve just a tad and heard a hissing sound and plus I could smell it. I quickly shut it off then. That is how I know it is flowing.

It is natural gas. I really don't understand as these lines are not new though. In order to replace the ventless heaters I just used the valve that is located at the ventless heater. Very confusing. I thought this would be a simple swap out.

But like I said, it was working for the previous heater. The previous heater broke because I couldn't turn the manifold valve to the on position any more.
 
  #5  
Old 10-03-20, 01:32 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
Once you replace the heater with a new one...... it could take at least five minutes or even more to purge the pilot line.
 
  #6  
Old 10-03-20, 02:04 PM
R
Member
Join Date: Oct 2016
Posts: 2,183
Received 199 Upvotes on 181 Posts
You’ll still have to check and adjust gas pressure. Gas burning equipment is not plug and play style appliances. And they do not come preadjusted.
Be careful with ventless equipment. There has been a lot of negative pressure out on them, and in some areas they’ve been outright banned due to safety issues. I’d suggest cracking a window or door when you use it, and don’t use it for a primary heat source.
 
  #7  
Old 10-03-20, 03:20 PM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
The garage I am using it in isn't very tightly sealed. I also have a CO alarm so should be fine. I removed the front cover and took two photos as you can see below.





 
  #8  
Old 10-03-20, 03:23 PM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
What exactly should I do to test and see if the pressure is ok?

Thanks
 
  #9  
Old 10-03-20, 03:29 PM
R
Member
Join Date: Oct 2016
Posts: 2,183
Received 199 Upvotes on 181 Posts
That tee with the plug is where you’ll take inlet pressure. There should be a plug in the valve for manifold pressure.
You’ll need a gas pressure gauge.
 
  #10  
Old 10-03-20, 04:41 PM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok, thanks. How do I adjust the manifold pressure? I found the below image in the installation instructions:




I also plan on using this to do the pressure testing:


From my understand I would simply remove the brass fitting on the end of the pressure gauge hose and push the hose onto where it says "outlet" on the gas manifold.

BTW: there are small screws located in the inlet and outlet of that gas manifold.
 
  #11  
Old 10-03-20, 04:45 PM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
Also from my understand where I circled red is where the inlet and outlet is located on that diagram:

 
  #12  
Old 10-04-20, 01:56 PM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
So I did manage to test the pressure at the Tee for the inlet and it read around 10 in. W.C. which should be very good. However, I don't know how to measure the Manifold pressure though.
 
  #13  
Old 10-04-20, 03:14 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
The manifold pressure is the outlet.
 
  #14  
Old 10-04-20, 04:54 PM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
There is a screw located in the outlet BTW. I placed the pressure gauge hose on the outlet and it read zero. I should also mention that I held down the pilot light for 20 minutes and still no spart happened.

Got any idea how I increase the pressure in the manifold as it is zero?
 
  #15  
Old 10-09-20, 08:16 AM
9
Member
Thread Starter
Join Date: Nov 2006
Location: USA
Posts: 148
Upvotes: 0
Received 0 Upvotes on 0 Posts
Believe it or not the gas heaters still are not working. Called the manufacturer and they said a part was busted. So went to store and got another gas heater and returned this one. Installed it. This one is having the same issue.
 
  #16  
Old 10-09-20, 07:23 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
On page 11 it discusses a "selector valve". Did you confirm that is locked in the NG postion ?
 
 