I have an April Aire 600 Humidifier and a Carrier 59TP6B Furnace and the wiring diagram that came with the Humidifier does not work. It is straight forward but I must be missing something, I have the Model 60 Humidistat, does anybody have a good wiring diagram for me. Any help is much appreciated as AprilAire offer no support at all.


This Diagram Produces No Result, no voltage is sent to the Solenoid.

R -------------------------R
C--------------------------COM 24V------------------------S
W-------------------------W/W1
gf (not used)
G (not used)
H--------------------------HUM 24V
H------------------------------------------------------------S
ODT---outdoor sensor
ODT---outdoor sensor









Thanks

Rich
 

Last edited by mppanj12; 12-11-20 at 09:32 AM. Reason: Update
  #2  
Old 12-11-20, 10:32 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,047
Received 3,419 Upvotes on 3,065 Posts
Welcome to the forums.

Basically you need to get 24v to the solenoid. It doesn't matter if you wire the yellow wiring exactly like I have it. You can switch the R or the C thru the HH terminals.

The W wire is what activates the humidifying process. Connect the to the HUM terminal.
Make sure that HUM terminal is 24vAC and not 120vAC.

 
  #3  
Old 12-11-20, 10:47 AM
M
Member
Thread Starter
Join Date: Dec 2020
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hi PJ,
How do I test the HUM Terminal on my furnace, I have a voltmeter and understand how to use it but I only have 1 HUM Terminal on my board, 1 lead to the HUM Terminal and where does the other lead go?
 
  #4  
Old 12-11-20, 10:53 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,047
Received 3,419 Upvotes on 3,065 Posts
The HUM terminal is switched and only comes on when the furnace is heating.

120v HUM is 120v from HUM to NEUTRAL (white push on terminals)
24v HUM is 24v from HUM to C where the thermostat wiring connects.

If you can't locate what you're looking for.... post the part number off the board.
 
  #5  
Old 12-11-20, 12:16 PM
M
Member
Thread Starter
Join Date: Dec 2020
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
PJ,

Does This Image Help, it took me a minute to figure this out but my image is on google.

Carrier Board

1. I should put 1 terminal on the HUM and the other on the COM if I get voltage that means it's probably 24V
OR
2.I should put 1 terminal on the HUM and the other on the White Fat Neutral Wire (isn't Com the same thing, Neutral) and I should get 120V

 
  #6  
Old 12-11-20, 01:02 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Hi, it does appear that your board does not have H H terminals, I would parallel the leads from the Humidistat up with W1 and C so when there is a call for heat and humidity is required the humidifier would operate.
Geo🇺🇸
 
  #7  
Old 12-11-20, 01:13 PM
M
Member
Thread Starter
Join Date: Dec 2020
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Dear G,
It has 1 HUM Terminal but not 2, according to the wiring schematics in the manual it's a 24v HUM terminal so I'm going to give it a try.
 
  #8  
Old 12-11-20, 01:26 PM
M
Member
Thread Starter
Join Date: Dec 2020
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
It worked in Test Mode, so far so good, thanks PJ and G.
 
  #9  
Old 12-11-20, 01:55 PM
M
Member
Thread Starter
Join Date: Dec 2020
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
This wiring method automatically opens up the Solenoid when the Furnace Ignites, this bypasses the Humistat which monitors the Humidity Levels. I want the Humistat to decide when it opens the solenoid and humidifies the home, any thoughts? I understand the HUM terminal is what gives power to the Humistat but the system is running like when the furnace ignites the water starts running regardless of the Humidity, any thoughts. Also, the Auto Fan Function is not working, supposedly when the Blower Activation is set to on it will turn on automatically if more moisture is needed, in test mode this is not activating.


Rich
 
  #10  
Old 12-11-20, 03:17 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,047
Received 3,419 Upvotes on 3,065 Posts
I don't allow the humidistat to force the blower on without heat with my installs.
Not enough moisture is transferred thru cold air.

If you want the humidistat to control the blower..... you'll need two more wires to the furnace board. You'd need to use the G and Gf terminals.

This wiring method automatically opens up the Solenoid when the Furnace Ignites, this bypasses the Humistat which monitors the Humidity Levels.
Power on the HUM terminal tells the humidistat that the furnace is in heating mode. Then it's the job of the humidistat to turn the humidifier on based on set and actual humidity. If the G and Gf aren't connected..... turn off the blower control. Make sure unit is not in test mode.
 
  #11  
Old 12-11-20, 03:54 PM
M
Member
Thread Starter
Join Date: Dec 2020
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks PJ,
I am giving this a try for 24 hours but I think it's working the way it's supposed too. You are a life saver, you have more knowledge than AprilAire and Carrier combined. Also, I installed a Scale Interceptor with strainer + .250 flow control, water is my expertise, lol. Thanks Again PJ.
 
 