3 Zone oil/hot water system. Zone 2 Thermostat is Programmed 68F most of the day other 2 zones much lower as little use during the day. Today Zone 2 was 74F and even when Thermostat was shut off manually, Zone kept getting hotter and furnace did not shut off. Am I correct to assume this is a Zone Valve or regulator that has gone bad?
 
  #2  
Old 12-24-20, 01:33 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
What type of zone valves?
 
  #3  
Old 12-24-20, 01:44 PM
MB McProc's Avatar
Member
Thread Starter
Join Date: Sep 2003
Location: Connecticut
Posts: 84
Upvotes: 0
Received 0 Upvotes on 0 Posts
  #4  
Old 12-24-20, 01:57 PM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Below where the wires connect should be a lever. Push the lever from side to side. If it moves with no resitance, the valve is stuck open.
 
  #5  
Old 12-24-20, 02:08 PM
MB McProc's Avatar
Member
Thread Starter
Join Date: Sep 2003
Location: Connecticut
Posts: 84
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes, when I first looked at it, it was in the middle, while the other 2 were on auto so I moved it to auto but I did slide it both ways no resistance first. Ok can I do anything about it myself?
 
  #6  
Old 12-24-20, 02:59 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,078
Received 3,422 Upvotes on 3,068 Posts
Since the valve is spring loaded closed and forced open by the motor..... it sounds like the gears are jammed. I usually pull the head off the valve to see if the valve will fully close with the head off. If it does.... replace the head. If it doesn't.... it may be time for a new valve to be installed.
 
  #7  
Old 12-25-20, 04:48 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 2,664
Received 235 Upvotes on 208 Posts
Is it possible one of the other two thermostats was calling for heat when you turned off the zone 2 thermostat and the furnace continued to operate? If not, either the zone 2 thermostat is bad or the zone control is malfunctioning.
 
  #8  
Old 12-25-20, 07:39 AM
MB McProc's Avatar
Member
Thread Starter
Join Date: Sep 2003
Location: Connecticut
Posts: 84
Upvotes: 0
Received 0 Upvotes on 0 Posts
I think we've pinpointed that it's definitely the Zone 2 Valve - We turned off the Furnace from the Emergency Switch overnight, but when we turned it on this morning to heat up the water, Zone 2 was up to 71F within 20 min. and would have continued rising if we hadn't turned it off. Putting in service call for tomorrow.

Merry Christmas everyone and huge Thank You for your support. MBProc & Family
 
  #9  
Old 12-26-20, 09:43 AM
D
Member
Join Date: Apr 2014
Location: us
Posts: 1,301
Received 100 Upvotes on 94 Posts
The zone valve switch may be bad.

Disconnect wires from switch. Put valve in Manual Open position.

That zone will get heat when one of others is activated. At least system is heating place.

Disconnect zone may get over heated, but rest of place will not be cold.
 
  #10  
Old 12-26-20, 10:06 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,078
Received 3,422 Upvotes on 3,068 Posts
If the end switch was bad... the boiler would run but the zone wouldn't get hot.
In this case the zone is getting hot when the valve is supposed to be closed
 
  #11  
Old 12-26-20, 05:33 PM
D
Member
Join Date: Apr 2014
Location: us
Posts: 1,301
Received 100 Upvotes on 94 Posts
Those tiny micro switches go bad with contacts either open or closed. DH has taken bad ones apart!

MB-M might just disconnect it, set valve to Manual Open, then see what happens. If that zone gets over heated would confirm bad switch.

MB_M instead of calling service and paying big $$$ might buy new power head for $56.

Heads are easy to replace, are held on by only 2 of 4 screws to valve body. Other 2 screws seal plate to valve chamber. Loosen them and get wet.

Click on Install Instructions in link for step by step how to. I buy a spare for cold winter nights.
.
https://www.supplyhouse.com/Honeywel...3E-Zone-Valves
 