Furnace cycling on and off because of APS

Sorry if a repeat, first one didn't go.
Carrier condensing
My furnace runs for a while then shuts down for a while. Maybe 10 minutes on then 15 off, and repeat over and over. I can make it run continuous by bypassing the air pressure switch. I have replaced the draft blower motor thinking maybe the draft was weak. No change. I put my hand next to the exhaust and I feel a good draft. When it runs everything seems good, flame color etc. I can't figure out what would make the air pressure switch shut it down after a while. My house only gets up to 55 degrees. I might replace the switch but doubt that is the issue. Any thoughts?
 
  #2  
Old 02-16-21, 03:50 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 2,663
Received 235 Upvotes on 208 Posts
From your description it seems the pressure switch is operational but maybe not to specification. Replacing the switch would be a cost saver versus obtaining the instruments to test the switch to specification or contracting for the same. Does the thermostat control the heating system normally when you bypassed the pressure switch?
 
  #3  
Old 02-16-21, 05:02 AM
R
Member
Join Date: Oct 2016
Posts: 2,135
Received 183 Upvotes on 169 Posts
DO NOT bypass safety controls. They are doing there job. I’ve seen fires caused by doing such things.
what’s the model number?
 
  #4  
Old 02-16-21, 07:41 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 2,663
Received 235 Upvotes on 208 Posts
Roughneck, I couldn't agree with you more. However I doubt there isn't a technician or DIYer out there that hasn't bypassed a device as part of their diagnostics. The DIYer in the above post, based on his words, seems to have knowledge of how a furnace control should operate and the consequences of his actions.
 
  #5  
Old 02-16-21, 08:51 AM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
The most common cause of pressure switch is vent pipe slope. The fact your furnace will run for about 10 minutes after a 15 minute rest tends to indicate a possible condensate drainage issue. If the vent has a slight belly in it somewhere that could certainly cause your issue.
 
  #6  
Old 02-16-21, 12:21 PM
L
Member
Thread Starter
Join Date: Feb 2021
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Today I was "lucky" enough to get another clue, there was water on the floor. The water sediment trap was full of sediment. I think cleaning that will fix it.
 
  #7  
Old 02-16-21, 01:40 PM
R
Member
Join Date: Oct 2016
Posts: 2,135
Received 183 Upvotes on 169 Posts
What is the model number of the furnace? Is it one of those affected by a class action lawsuit? That one of the symptoms is solids in the condensation?
 
  #8  
Old 02-16-21, 02:40 PM
L
Member
Thread Starter
Join Date: Feb 2021
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Gee, I wonder. Model # 398aaw036060d
I had the heat exchanger replaced a few years ago and at the time the guy who did it said the exchanger was under warranty but his labor was not.
 
  #9  
Old 02-16-21, 03:57 PM
R
Member
Join Date: Oct 2016
Posts: 2,135
Received 183 Upvotes on 169 Posts
That unit isn’t affected.
However, drain cleaning is something that should be done during preseason maintenance that needs to be done every year.
 
  #10  
Old 02-16-21, 04:04 PM
L
Member
Thread Starter
Join Date: Feb 2021
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for checking. I appreciate it.
 
  #11  
Old 02-16-21, 09:54 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,044
Received 3,417 Upvotes on 3,064 Posts
It's almost impossible to bypass the pressure switch. If you short around it..... the board will show a "closed" pressure switch and will not light. It needs to see the pressure switch open on a call for heat and then go short when the inducer runs. It's designed so that it can't be bypassed permanently. It can be bypassed as a one shot test.
 
  #12  
Old 02-16-21, 10:02 PM
L
Member
Thread Starter
Join Date: Feb 2021
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Right, I discovered that. First time I did it I was measuring voltages and finding where the fault was and just jumped it. Next time on cold start it didn't like it, but I already had got some heat into the house.
Lee
 
 