Furnace exhaust fan running...


  #1  
Old 04-14-21, 09:32 PM
D
Member
Thread Starter
Join Date: Apr 2021
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Furnace exhaust fan running...

I have an older York plus furnace if I leave the furnace on for a period of time the exhaust fan continues to run after it is cycled off the only way to shut it down is to turn thermostat off or switch by furnace off for a few minutes once I turn it back on or turn the thermostat back on furnace will fire up in normal sequence it will stay running till heat is reached turn off and may cycle correctly for a few cycles but then goes back to leaving the exhaust fan on constant and I’ll need to shut everything down again... any help would be appreciated...
 
  #2  
Old 04-15-21, 06:25 AM
R
Member
Join Date: Oct 2016
Posts: 2,137
Received 185 Upvotes on 169 Posts
What is the model number?
What error is shown while the unit is having this issue?
 
  #3  
Old 04-17-21, 04:47 AM
D
Member
Thread Starter
Join Date: Apr 2021
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
No error code... 20+ years old...

Mode # p2udd12n095001c



 
  #4  
Old 04-17-21, 05:19 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Hi, is there a wiring Dia that you can post?
Geo 🇺🇸
 
  #5  
Old 04-18-21, 05:15 PM
D
Member
Thread Starter
Join Date: Apr 2021
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sorry no wiring diagram...
 
  #6  
Old 04-18-21, 05:24 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,067
Received 3,422 Upvotes on 3,068 Posts
Disconnect the W wire off the control board.
If it still remains running.... the draft inducer relay may be sticking requiring a board replacement.

What are you using for a thermostat ?
There are several power stealing (smart/wifi) types that can cause a drain on the W line keeping the inducer running.
 
 