C wire from gas furnace to nowhere ...


  #1  
Old 06-10-21, 03:19 PM
D
Member
Thread Starter
Join Date: Nov 2004
Location: san diego, ca
Posts: 145
Received 0 Upvotes on 0 Posts
C wire from gas furnace to nowhere ...

I currently have a thermostat that does not have a C wire connection. I was given a smart thermostat that says it is designed to work without a C wire but in some cases one will be needed. I checked the circuit board on the gas furnace and there is a wire coming from the C wire connection. Will the C wire be in the wall behind the thermostat? Why would they have it going from the gas furnace but not to the thermostat? The gas furnace was installed in 2014. I assume the thermostat was as well (seems like a fairly recent model - Honeywell). The house from the early 70s.
 
  #2  
Old 06-11-21, 09:30 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,051
Received 3,419 Upvotes on 3,065 Posts
Please post pictures of your wiring....... How-to-insert-pictures.
We need to see the wiring at the thermostat and the furnace board.

If you look at the wire currently on the C terminal..... you'll probably see that it goes to a two wire cable. The other wire in that cable would go to Y. That is going to the A/C condenser outside.
 
  #3  
Old 06-11-21, 02:04 PM
D
Member
Thread Starter
Join Date: Nov 2004
Location: san diego, ca
Posts: 145
Received 0 Upvotes on 0 Posts
Here are the pictures. 2 wires coming out of Y. What does that mean? The C wire goes to the Y terminal?



 

Last edited by PJmax; 06-11-21 at 05:57 PM. Reason: resized/labeled pic
  #4  
Old 06-11-21, 06:01 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,051
Received 3,419 Upvotes on 3,065 Posts
If you look at the wire currently on the C terminal..... you'll probably see that it goes to a two wire cable. The other wire in that cable would go to Y.
As I described..... you have two cables at the furnace.
One goes to the thermostat and one goes to the A/C condenser.

The four wire thermostat cable is....
Red - R
Yellow - Y
Green - G
White - W

The five wire A/C condenser cable is.....
White - C
Yellow - Y
Blue, red, green are spares.
 
daufoi voted this post useful.
  #5  
Old 06-11-21, 07:08 PM
D
Member
Thread Starter
Join Date: Nov 2004
Location: san diego, ca
Posts: 145
Received 0 Upvotes on 0 Posts
Thanks PJ Max. I hope the new thermostat works without the C wire. What do you mean they are spares?
 
  #6  
Old 06-11-21, 08:12 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,051
Received 3,419 Upvotes on 3,065 Posts
If you look at the condenser cable.... you'll see three wires wrapped around the jacket. Those are spares since it's a five wire cable and only two wires were needed. To bad they didn't run the same wire to the thermostat.
 
 