Trane xr80 gas furnace


  #1  
Old 08-11-21, 09:09 AM
W
Member
Thread Starter
Join Date: Aug 2021
Posts: 4
Upvotes: 0
Received 1 Upvote on 1 Post
Unhappy Trane xr80 gas furnace

I noticed a loud noise coming from my furnace. I went to take a look and discovered my draft inducer was running while the cool mode is on, the ignitor nor gas kick on, thank goodness. I have checked the wiring. In the last several months I had to replace the board due to water damage. The draft inducer should not run when in cool mode. I shut down the breaker for about 20 minutes, hoping a reset would happen. Any other possibilities?

BLW00889 draft inducer Fasco D341663PO5
Trane XR80
 
  #2  
Old 08-11-21, 09:26 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,022
Received 3,409 Upvotes on 3,059 Posts
Welcome to the forums.

Go to the furnace board and remove the W wire. (W1 and W2 if it has two).
Does the inducer still run by itself ?
If yes..... there is a board problem or failure.
 
  #3  
Old 08-11-21, 09:58 AM
R
Member
Join Date: Oct 2016
Posts: 2,131
Received 183 Upvotes on 169 Posts
Are you using a Neest thermostat?
 
  #4  
Old 08-11-21, 03:26 PM
W
Member
Thread Starter
Join Date: Aug 2021
Posts: 4
Upvotes: 0
Received 1 Upvote on 1 Post
Not using a nest. Using a Honeywell RTH6580WF.

Pete... When I disconnect the W on the furnace board, the inducer does run. So it may be the board. Great tip.I do not get any errors on the LEDs.

I have 5 wires out of the wall to the thermostat. Blue, R, G, Y, W. I bypassed the Blue common and moved G to C and jumped Y to G on the furnace. I jumped because I get nothing using the Blue common. Weird, but good thing I could jump.
 

Last edited by Wilder1121; 08-11-21 at 03:48 PM.
roughneck77 voted this post useful.
  #5  
Old 08-11-21, 11:17 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,022
Received 3,409 Upvotes on 3,059 Posts
Not quite following you.
The blue wire you were using as common is now open ?
Or is it not connected to the right location.
 
  #6  
Old 08-12-21, 10:30 AM
W
Member
Thread Starter
Join Date: Aug 2021
Posts: 4
Upvotes: 0
Received 1 Upvote on 1 Post
hi pete. Bl is not connected at either end.
 
  #7  
Old 08-12-21, 10:53 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,022
Received 3,409 Upvotes on 3,059 Posts
Ummmm..... ok. I guess eventually you'll be connecting it since you need it.

You've confirmed a board problem which is strange since you just replaced it.
Confirm that the inducer is connected to the proper terminals on the board.
 
  #8  
Old 08-13-21, 04:02 PM
W
Member
Thread Starter
Join Date: Aug 2021
Posts: 4
Upvotes: 0
Received 1 Upvote on 1 Post
Hi Pete,
I wanted to share the troubleshooting information I got from White Rodgers on the board, incase you see something similar on the forum later.

In the furnace:
Please check on a call for cool if you are getting 24 volts from W to ground.
-if you are getting 24 volts on W isolate the thermostat, remove W wire on the thermostat
-if 24 volts disappear, problem is the thermostat.

Check Inducer and Inducer Neutral on the 4 pin and check if you are getting 120v.
If there is no 24volts on the W terminal and the draft inducer is coming on during a call for cool, problem is the furnace control board.
 
 