I have an intermittent problem where the ignitor is not getting power when the furnace starts up.
I was thinking it could be the pressure switch or the board.
I used my multimeter to test the wire lead to the ignitor for voltage. There is no voltage. The ignitor itself shows 80 ohms of resistance.
I was testing to see if the pressure switch circuit was properly closing during the furnace start up sequence. Per a YouTube video created by an HVAC professional, I put a multimeter lead on each of the pressure switch terminals and set the multimeter to test for continuity. Per the video, when the pressure switch circuit closed the multimeter would alarm for continuity.
I turned on the furnace, and the continuity test blew the panel fuse.
During the furnace start up, the gas valve does open but of course, it closes again if the ignitor does not turn on. So perhaps the pressure switch is not the issue.
What could be causing the ignitor to not get any power ?
Last edited by jsbigger; 11-10-21 at 06:40 AM.
Reason: clarify
You can't use continuity on a live circuit. You put your meter in AC volts. Connect the leads across the pressure switch. You should measure 24vAC. When the inducer is running you should measure 0v across the pressure switch. If the switch doesn't close.... the igniter won't heat.
Pull the pressure switch hose off. Check the hole where the hose connects to the inducer or burner chamber. There is typically a small hole all the way down INSIDE the fitting. That needs to be cleaned with a pin or small piece of wire or drill bit.
I recently replaced the pilot tube and pilot burner in my Coleman propane furnace and it now works as it should. The two 10-32 screws that hold the pilot shield to the pilot/thermocouple bracket and burner assembly were rusted and very difficult to break loose.
I want to replace those rusted screws so if I ever need to remove them again it won't be so difficult. Should I use stainless screws - or - (because I think the bracket is not stainless) is galvanic corrosion a concern?
F80CTL Carrier/ICP 45,000 BTU nat gas furnace install. Due to the small space being heated, we were advised this is the smallest we can get, but we should run it single stage only, at 29,000 BTUs, so that we eliminate risk of overheating the unit. What wiring/dip switch/jumper changes need to be made to accomplish this? We have a basic, single stage thermostat currently for the old here which died recently. Many thanks.