Limit switch function

I was having a problem with my blower motor not turning on. I changed the combination fan and limit control Honeywell l4064 and it was still acting up. I then jumpered the heater fan control pictured below and its working fine. I think its supposed to close at 110degrees? Its a few feet above the heat exchanger. Isn't the combination fan and limit control supposed to control the fan on/off at 100/130 degrees also?


 
  #2  
Old 11-21-21, 10:26 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
The combo fan/limit control is typical what control the blower.
The switch in the picture is also a fan switch.
F110-2 stands for fan control - close at 110° and open at 90°.
Those switches are not normally wired in thermostat cable.

I'd need a wiring diagram of your furnace to comment further.
 
 